Discuss Neutral to CPC low reading on lighting circuit EICR in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Dartlec

Esteemed
Arms
Reaction score
2,441
Typically the EICR I fitted in this afternoon because I'd hoped it would be fairly simple (new build home, 2007), turned out to be the only recent one that's thrown up a major FI.

Downstairs lighting circuit, 1mm T&E, currently on a 6A MCB

R1+R2 fine, insulation test L&N -> E an immediate 0.0MOhm

Removed every lamp and still getting 0.26 Ohm resistance Neutral to Earth.

L-N and L-E both test >999 MOhm

With some further isolation I managed to narrow it down to what appears to be a single run between the ceiling fitting in the back room (3 plate wiring) and the adjacent kitchen switch (2 plate wiring) and fairly sure there's nothing else in between in terms of fittings.

Am I missing anything obvious, or does this sound like nail/screw through the cable bridging N & E?

The house has been ill treated by tenants, but no obvious signs that the wiring has been tampered with - though odd how they used loop in wiring in one room and neutral at switch in the other rooms....

Does go to show the value of doing a proper EICR though - Live testing only would have missed this - though it would have bitten anyone in the arse who had just put RCD board in without properly testing first....
 
Test at every accessible point N to E, you might be able to narrow the location down. Possibly with careful measurements and luck to an approx. distance between the two lowest results.

To add, if one of the rooms is a kitchen, any possibility of unused cabling e.g. for cabinet lights not fitted, cables hidden behind wall units. Perhaps even a wall unit screw through a cable.
 
Test at every accessible point N to E, you might be able to narrow the location down. Possibly with careful measurements and luck to an approx. distance between the two lowest results.
Not long been home but was planning to dig out the resistance tables and try to work out how far 0.12 Ohm is on 1mm - the last reading I got from one end of what I think is the dodgy leg- it's a new build so board not floorboards and of course downstairs lighting, not nicely in the loft....:rolleyes:

I was doubting myself at one point, but definitely getting the readings with the circuit totally disconnected from the CU end and failing IR with or without earth connected, so only thing I can see it being is a screw or nail through the cable - might even have been there since it was built...

Fortunately property is currently empty so could leave it off until I can work things out...
 
There are words for that incoming supply but I would not like to use them in case ladies are present
I've seen similar in a new build completed within the last year too - except it was carpet that time.

Wonder what the common denominator could be cough new build cough.

I'm assuming the floor layers followed the DNO install and cut the floor round it, but even on the base floor the DNO shouldn't have connected it - I'll be using SWA clamps on it I think, but that can only mitigate it so far.

Anyone do an earthed steel version of this? ?

indoor-cable-protector.jpg
 
To add, if one of the rooms is a kitchen, any possibility of unused cabling e.g. for cabinet lights not fitted, cables hidden behind wall units.
That's exactly what it was last time I had this. I've also known front door / back door outside lights removed and cable literally sawn off at the wall, shoved back 5mm and sealed over.
I guess you've had every light switch off by now but an earthed back box and a facia screw through the N is another contender.

BTW I make it about 2.7m if that measurement was 2 x 1mm cores (as opposed to a nulled wander lead)
 

Reply to Neutral to CPC low reading on lighting circuit EICR in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
645
Hi Im an apprentice and just wanted to clarify domestic style wiring since i work industrial and don't deal with conventional wiring. in college...
Replies
1
Views
904
M
Hi Guys I purchased some of the above online around 3 weeks ago, They are a fairly new product, very usefull as you can change both colour from...
Replies
1
Views
314
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
814
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
629

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock