Typically the EICR I fitted in this afternoon because I'd hoped it would be fairly simple (new build home, 2007), turned out to be the only recent one that's thrown up a major FI.
Downstairs lighting circuit, 1mm T&E, currently on a 6A MCB
R1+R2 fine, insulation test L&N -> E an immediate 0.0MOhm
Removed every lamp and still getting 0.26 Ohm resistance Neutral to Earth.
L-N and L-E both test >999 MOhm
With some further isolation I managed to narrow it down to what appears to be a single run between the ceiling fitting in the back room (3 plate wiring) and the adjacent kitchen switch (2 plate wiring) and fairly sure there's nothing else in between in terms of fittings.
Am I missing anything obvious, or does this sound like nail/screw through the cable bridging N & E?
The house has been ill treated by tenants, but no obvious signs that the wiring has been tampered with - though odd how they used loop in wiring in one room and neutral at switch in the other rooms....
Does go to show the value of doing a proper EICR though - Live testing only would have missed this - though it would have bitten anyone in the arse who had just put RCD board in without properly testing first....
Downstairs lighting circuit, 1mm T&E, currently on a 6A MCB
R1+R2 fine, insulation test L&N -> E an immediate 0.0MOhm
Removed every lamp and still getting 0.26 Ohm resistance Neutral to Earth.
L-N and L-E both test >999 MOhm
With some further isolation I managed to narrow it down to what appears to be a single run between the ceiling fitting in the back room (3 plate wiring) and the adjacent kitchen switch (2 plate wiring) and fairly sure there's nothing else in between in terms of fittings.
Am I missing anything obvious, or does this sound like nail/screw through the cable bridging N & E?
The house has been ill treated by tenants, but no obvious signs that the wiring has been tampered with - though odd how they used loop in wiring in one room and neutral at switch in the other rooms....
Does go to show the value of doing a proper EICR though - Live testing only would have missed this - though it would have bitten anyone in the arse who had just put RCD board in without properly testing first....