Discuss never seen before building earthed via trunking in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
18
hello all in my considerable yrs ive never come across a building earthed via trunking all circuits lights power earth taken back to nearest trunking and terminated no earths at board even main earths for 5x different panels back to trunking is this legal in todays regs ?
 
The wiring regs aren't a legal requirement. Using containment as a CPC is permitted by the wiring regs. The usual rules for protective conductors apply with regards to thermal constraints and sizing etc. Of course the integrity and condition of the containment and all associated couplings and joints is essential.
 
It is not legal in the regs, nothing is legal in the regs, the regs have no legal status.

It can comply with regulations if the requirements of the regulations are met, if they are not then it does not comply.

Use the adiabatic equation to calculate the required CSA of a steel CPC and then compare that to the actual CPC, this will tell you whether it is the right size or not.

Then measure the Zs using a high current test and this will tell you whether that complies or not and give an indication that all connections are sound.

ideally you would use a ductor type high current milliohm meter to confirm the soundness of the connections but they aren't so commonly available to us humble electricians any more


Sent from my iPad using Tapatalk
 
Not common now but I have done this back in the 80s. We installed separate cpcs through the conduits to socket outlets etc and bolted them to the trunking. Don't know why I can only assume that as the trunking had straps across each joint but the conduit connections did not it ensured good continuity. Can't beat using containment as a cpc.
 
Not common now but I have done this back in the 80s. We installed separate cpcs through the conduits to socket outlets etc and bolted them to the trunking. Don't know why I can only assume that as the trunking had straps across each joint but the conduit connections did not it ensured good continuity. Can't beat using containment as a cpc.

I remember doing this in the 80s as well we had copper links to put over the screws on the couplers.
 

Reply to never seen before building earthed via trunking in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
656
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi all, For clarity, I'm not a qualified electrician, but have a reasonable amount of experience as I've done plenty of wiring (signed off by a...
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock