Discuss New bedroom wiring in the UK Electrical Forum area at ElectriciansForums.net
Ok so pretty much the cable from new double socket into a 5a fuse then run lights and extractor of of thatYou can, but the lights and the fan will need another fuse, to limit the current to 5or6 amps.
Typically you would use a FCU (fused connection unit) for fusing down the supply for lights in such a scenario, as most light switches are rated at 10A and some lights specify a maximum over-current protection value for safety.
The lights are unlikely to need more than an amp or so anyway, so it may well be practical to use a 3A FCU for supplying both the lights and fan, with the fan simply on an isolation switch.
Just to confirm the layout is correct.Is the socket outlet part of the ring final circuit, is the socket already spurred from the ring final circuit or is the socket part of a radial circuit.
5a/6aDoes the fan manufacturer specify a 5A fused supply?
Seems unusual.
5a/6a
Ok thats coolI don't wish to sound uncharitable, but I don't believe that for one second and suspect those numbers have been lifted from post #2, after you originally asked if it was okay to run the fan and lighting from a 13A fused spur.
Ensure the fan is installed in accordance with the manufacturer's instructions, regardless of who installs it, as failure to observe those instructions could result in fairly dire consequences.
**I'm not an electrician, but simply someone concerned by what you've posted**
I fitted a fan not that long - I think it may have been an Xpelair - that did specify a 5A fuse in the MI, which is unusual as they often seem to state 3A.Does the fan manufacturer specify a 5A fused supply?
Seems unusual.
Assuming the existing socket circuit is a Ring Final Circuit (on a 32A breaker), then unfortunately that is a spur off a spur which isn't compliant -Just to confirm the layout is correct.
Spur taken from double socket off final curcuit. To a 30a fused wall box then to 1x double socket to 5amp fused box 3 core + earth to led light then on to extractor. from light to switch and thanks much appreciated
Same fanI fitted a fan not that long - I think it may have been an Xpelair - that did specify a 5A fuse in the MI, which is unusual as they often seem to state 3A.