Discuss New Build Electrical Installation queries in the Industrial Electricians' Talk area at ElectriciansForums.net

M

mstoker1990

Good Morning Folks

I think I can pretty much answer my own question however some different opinions would be good and if anyone could quote the reg no.s for the answers that would be sound as mine is still boxed up somewhere.

I have just bought a new build property.

Issue Number one.
All Downlighters are fire Rated GU10 with twin and Earth Connected direct with cables stripped further back than the cable clamp....Single insulated cables on show....A Fail Yes?

2
Consumer unit is on a sub main fed via the cheapest looking switch fuse I have ever seen in the meter box with the 16mm twin and earth stripped as it enters the meter box with single insulated cores entering the switch fuse and a taped up earth going to the earth block. a seperate 10mm earth does accompany this.

3
The Smoke Alarms are on the same group RCD that powers Socket outlets, I always believed smoke Alarms should be on there own dedicated circuit or if RCD protection was needed either an RCBO would be needed or it could go on a group RCD not supplying Smoke Alarms.

Let me know your thoughts, the house is built by a well known builder and some of the workmanship from all trades is beyond shocking!!
 
1 and 2, i agree. bad workmanship. non compliant with BS7671. as for 3. it's common to wire smoke detectors on a lighting circuit. you'll know if the feed is down as the lights won't work.
 
Not surprised about 1 & 2 - cutting corners and using cheap installation methods will always happen.

3 - absolutely nothing wrong with this - what makes you think otherwise?
 
1. A bit rough but very common.

2. Very rough.

3. Quite normal and if you get back from a long holiday and the power to the smoke alarms is off, you'll notice as the lights won't be working either.
 
apprfopriate regs. for 1. and 2. would be 526.5 and 526.8, BS7671 (2011) green book.
 
As for 3. Smoke alarm with battery backup or Grade D, can be feed from RCD on lighting circuit only. Mains only smoke alarms or Grade E, must be on the own circuit with lockable isolation,
 
apprfopriate regs. for 1. and 2. would be 526.5 and 526.8, BS7671 (2011) green book.


Many Thanks for your responses.

I've always been told since the 17th Came in to place that smoke alarms should not be put on the same RCD that supplies socket outlets, Dont know why, I suppose i maybe work to higher standards than those in the new build game.
I always put an RCBO next to the main sw on a board for smoke alarms.

If someone tells me how to put pictures on here I will upload them?

Many Thanks.
 
Many Thanks for your responses.

I've always been told since the 17th Came in to place that smoke alarms should not be put on the same RCD that supplies socket outlets, Dont know why, I suppose i maybe work to higher standards than those in the new build game.
I always put an RCBO next to the main sw on a board for smoke alarms.

If someone tells me how to put pictures on here I will upload them?

Many Thanks.

I would never do that. It gives the residents the ability to switch them off. Stick them on a ligthing circuit!
 
Many Thanks for your responses.

I've always been told since the 17th Came in to place that smoke alarms should not be put on the same RCD that supplies socket outlets, Dont know why, I suppose i maybe work to higher standards than those in the new build game.
I always put an RCBO next to the main sw on a board for smoke alarms.

If someone tells me how to put pictures on here I will upload them?

Many Thanks.

get image on desktop. then in reply box, 3rd icon from right "inseret image". select from computer, choose file upload. done.
 
How long is this 16mm T&E submain?? Never understood using T&E to supply Houses and flats in a multi dwelling supply set-up. It just smacks of a cheap and nasty install in my book!!
 
No, it needs to comply with 522.6.103


True Which states if mechanical protection by earthed metallic conduit or trunking is not in place and cables are less than 50mm in walls or partitions then RCD protection is required..

BTW its , 522,6,203 in the BYB
 
Still wont let me upload the images, just states which URL to use.

Fully agree, Dont know whether the Twin and Earth runs in the cavity or behind the plasterboard on the backside of the meterbox. If this is the case it wouldnt even be in a safe zone nevermind needing RCD Protection.

The Twin and Earth Probably runs about 6-7Metres
 
i had that problem some time ago. would only allow pics from url, and not from computer. could be a browser problem. pm marvo or sintra.to see if it can be sorted
 
To be a pedant, the requirement to provide additional protection for cables concealed in walls, allows for:
Installing at a depth greater than 50mm.
Earthed metallic sheathing.
Earthed conduit or trunking.
Mechanical protection sufficient to prevent penetration by screws or nails.
By running cables in prescribed zones and providing 30mA RCD protection.

Always seemed odd to me that only the last option requires the cables to be run in prescribed zones.
 
To be a pedant, the requirement to provide additional protection for cables concealed in walls, allows for:
Installing at a depth greater than 50mm.
Earthed metallic sheathing.
Earthed conduit or trunking.
Mechanical protection sufficient to prevent penetration by screws or nails.
By running cables in prescribed zones and providing 30mA RCD protection.

Always seemed odd to me that only the last option requires the cables to be run in prescribed zones.

It's not that odd when you look at the history of it, the bit about RCDs was pretty much just added on to the end of the existing regulation. The bit about the safe zones was always there, it's just adding the RCD that was new.
 
Please can we see some photos?
From what you have described:

1 and 2 yes, that sounds absolutely disgusting that someone has done work like that. It pains me that people are being allowed to work as an electrician without being competant and fully trained during a proper apprenticeship. Electrical work is for professional people, not monkeys who don't care or understand what they are doing. My opinion is that the individuals who did this work should be traced and banned from electrical work/prosecuted and fined.

As for 3, it is standard procedure to put smoke alarms of the lighting circuit - one of the reasons is, as another poster said, if the lights are not working you know the feed is off. I do wish there were National/International standards of practice for electrical installation.
 

Reply to New Build Electrical Installation queries in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hello. I live in a new build house with a separate garage. The garage is connected to RCD in the house to a 16A circuit breaker. The cable from...
Replies
1
Views
170
Hi folks, I have recently had a 5kW Solis inverter and 15kW/hr of batteries installed. Everything is working fine, but I have some concerns about...
Replies
3
Views
335
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
11
Views
441
We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock