It is a mission to get a 16mm into a single phase boards and a 70mm will be mission impossible. Just the gland for a three core would be 40mm.
 
Last edited:
I don't expect the load at any kiosk to exceed 10A, except for the last kiosk which will be around 40A I would suspect, but again, there may be more in the future (there is a barn close to the final kiosk which will likely want lighting and sockets in eventually.

I have decided to go for an 100A switched fuse after the meter. 100A main isolator in kiosk 2 and 3. With the feed from kiosk 2 down to 3 via an 80A MCB. Then from kiosk 3 to the final kiosk via a 63A MCB. All lighting circuits on MCB and the rings on RCBOs. At the final kiosk will be a 30mA RCD which will feed a future ring and lighting,it will also
If you expect 10A max or so then why a 80A MCB???

Also you won't get very good selectivity with MCB/fuse, and none guaranteed if 100A fuse and 80A MCB!

Though to be fair you probably won't have a PFC/PSSC high enough by the end to cause problems (e.g. Hagar say 63A B MCB of the NBN commercial B-curve is selective to 4.3kA with a 100A BS88 fuse).

Really you would be much better putting in 63A switch-fuses for each kiosk and then your choice of 32A/6A RCBOs, etc. Then you get selectivity with your incoming & the DNO fuses, can safely run 16mm or 10mm from the output of the switched fuse to the kiosk, and the final circuits are selective to around 1.1kA for faults on the ring not taking out the 63A fuses (again, based on Hager guide and that by the far end I doubt you will be seeing much more than 1kA or so PFC).
 
So because there may be a very slim change of the main fuse blowing with a 63A fuse in the SFI, then you choose to do no selectivity whatsoever... Interesting.... Not something I would do.
A fault that is going to blow the 80A fuses is also likely to blow the 100A fuses you get no realistic discrimination . There's no point in limiting yourself further down stream by starting with 80A fuses.
 
New posts

Reply to New circuit design question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
899
I'm after advice on how best and safely to do a friends Fuseboard upgrade. Current setup is a Wylex 6 Way board with MCBs of 2x 6A, 2x 32A and 30A...
Replies
2
Views
272
Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
680
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
570

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock