Discuss New circuit to detached shed/garage in garden. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

I just like how only the other year when i was mentioning part p and enquiring if it was a qualification people were quick to slam it and say it wasnt anything....yet here some people are on here defending someone who says one if their qualifications is part p....make your mind up
 
Just do it properly and run the cable down to the shed in SWA cable buried at a sufficient depth backfilled correctly with warning tape over to an RCD consumer unit in the shed. Forget this bodged job of PVC cable in buried trunking under slabs. Sounds like one of Pete's boil in the bags.
 
If the OP has, as he claimed, passed his 2382-18 then he should know that the sockets need to be protected by a RCD; if he's his Part P, then he should know the job will need notifying first; the source may be an addition to the house circuit but it's a new installation into the detached garage, so he's putting a new installation in a 'Building Sharing a Supply with Dwelling' and a 'Detached Shed, Garage or Greenhouse'

His suggestions of using steel trunking in the ground (where it will rust away) and of using T&E in trunking tells me he shouldn't be doing any electrical work.

"However I checked his ring and there is not much on it." doesn't mean a thing, you have to calculate the circuit load allowing for diversity, after all the next occupier/next year, may have much more attached to it.

He says there's no water services to the garage but does it have ANY extraneous conductive parts?

This, as has been said, should be done properly as a sub main from the house CU to a GCU. It needn't mean lifting 40 slabs as the armoured cable could be clipped on the outside of the house wall/under the eaves etc, to the point where the OP is thinking of routing to the garage; or a 6mm T&E could be run into the roof void, across to that point, then junction to the armoured to come down the wall (e.g. behind a drain pipe?).
Please educate me in how you notify electrical work before it is tested and completed ?? i.e not even started !!
 
If the OP has, as he claimed, passed his 2382-18 then he should know that the sockets need to be protected by a RCD; if he's his Part P, then he should know the job will need notifying first; the source may be an addition to the house circuit but it's a new installation into the detached garage, so he's putting a new installation in a 'Building Sharing a Supply with Dwelling' and a 'Detached Shed, Garage or Greenhouse'

His suggestions of using steel trunking in the ground (where it will rust away) and of using T&E in trunking tells me he shouldn't be doing any electrical work.

"However I checked his ring and there is not much on it." doesn't mean a thing, you have to calculate the circuit load allowing for diversity, after all the next occupier/next year, may have much more attached to it.

He says there's no water services to the garage but does it have ANY extraneous conductive parts?

This, as has been said, should be done properly as a sub main from the house CU to a GCU. It needn't mean lifting 40 slabs as the armoured cable could be clipped on the outside of the house wall/under the eaves etc, to the point where the OP is thinking of routing to the garage; or a 6mm T&E could be run into the roof void, across to that point, then junction to the armoured to come down the wall (e.g. behind a drain pipe?).
Please educate me in how you notify electrical work before it is tested and completed ?? i.e not even started !!
 
New posts

Reply to New circuit to detached shed/garage in garden. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
292
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
890

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock