Discuss New CU but no water bonding... in the UK Electrical Forum area at ElectriciansForums.net

jaydub

-
Reaction score
24
Someone has asked for an upgrade to their consumer unit but they have no water bonding. I explained this and said it needs to be done but it's quite a job and they don't want it done, just the CU upgraded?

What's the crack with that?

Can you crack on and put it down as a departure from bs7671?
 
Someone has asked for an upgrade to their consumer unit but they have no water bonding. I explained this and said it needs to be done but it's quite a job and they don't want it done, just the CU upgraded?

What's the crack with that?

Can you crack on and put it down as a departure from bs7671?
Or walk away, safety should have no cost if they wont pay walk away.
 
So the IET come out with regs, make no attempt to publicise the regs and leaves the poor sparks to educate the public.

This is not acceptable.

So, our responsibility is to make sites safer and, as such, updating a cu to one with. MCB's and RCD's is making the site safer.

Tin hat on

Just saying..

Ps. None of the CPS make any attempt, that I am aware of to educate Joe public either.

My advice to the op is to provide a written quote with the cu and bonding update ... Then see what happens.....
 
Thanks everyone, just a situation I have not yet come across.

Can anyone give me an example of when you might use the departures section? Just out of interest really. Again, never used it or seen it used!
 
sometimes you canfind a cold water pipe in an easier location to bond. in that case, it could be noted as a departure, as long as a R2 test confirmed that said bond had an acceptable resistance to the pipe where you'd have liked to bond ( i.e. close to the point of entry ).i done that with the gas here. as the main gas pipe passess next to the CU. the entry point is 10yards away in the attached garage.
 
Reg 528.3.4

ii) Fault protection shall be afforded in accordance with the requirements of section 411.

If I'm completely off target, please feel free to tell me, I'm here to learn. As far as I'm aware, if you can't guarantee you electrical services, are not in close proximity with other services, section 411 applies?
 
Reg 528.3.4

ii) Fault protection shall be afforded in accordance with the requirements of section 411.

If I'm completely off target, please feel free to tell me, I'm here to learn. As far as I'm aware, if you can't guarantee you electrical services, are not in close proximity with other services, section 411 applies?
Yes but that's nothing to do with main protective bonding of extraneous parts :mtongue::) although it is part of ADS
Chapter 54 deals with protective bonding
 
Last edited:

Reply to New CU but no water bonding... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
879
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
750

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock