Discuss New Distribution Circuit to existing consumer unit in the UK Electrical Forum area at ElectriciansForums.net

T

Toneyz

Do not know all details but Contracts Manager we know has had EICR done (not seen it yet) but the attached garage has a socket in it not sure if it is on ring or just spurred off ring into garage but a plastic 2/4 way PLASTIC consumer unit has been installed fed from this circuit containing 2 x 16A mcb's feeding sockets in conservatory the EICR has picked this up and he has asked us to put a new supply to feed this from existing main consumer unit as this report should have picked up plastic C.U.. Now my question is although I am installing a new sub-distribution circuit to the garage c.u I am not required to replace the existing garage plastic C.U. am I.
 
Only your new installation work needs to comply to bs 7671 it’s not an issue if an existing consumer unit is plastic as they are millions out there and there is no need to change to metal unless you are installing one yourself.
New circuits can be added to a plastic consumer unit no problem if it’s in an acceptable condition and can except the added load/circuit.
If it’s fit for purpose then leave it be.


As for the report it’s not necessarily a requirement to code the plastic consumer unit unless it’s believed to warrant a code or maybes just a note in the comments section of the eicr
 
Last edited:
It will be removing 2.5/1.5 T&E spurred off garage socket feeding garage existing plastic c.u. in garage and installing new supply (sub dist. circuit) to it from main c.u..
 
Then if the consumer unit is in an acceptable condition it can be left.
Just make sure your distribution circuit complies , adequate circuit protection, reference methods etc.
If your using swa as the distribution circuit then maybe you might not be able to gland in the cu so metal maybe an alternative but not necessarily essential.
 
Then if the consumer unit is in an acceptable condition it can be left.
Just make sure your distribution circuit complies , adequate circuit protection, reference methods etc.
If your using swa as the distribution circuit then maybe you might not be able to gland in the cu so metal maybe an alternative but not necessarily essential.
It is a old Tenby C.U as main C.U. and garage c.u has 20mm K.O's so can have earth nuts both ends.
 
So you have a socket in the Garage, with a spur from that socket feeding a Consumers unit in the Garage correct? Sounds like a bit of a bodge job Ant, and he wants you to run a new larger supply from the Main C/U to feed the Garage C/U again is that correct? what is intended to be fed from the newly supplied Garage C/U?
 
So you have a socket in the Garage, with a spur from that socket feeding a Consumers unit in the Garage correct? Sounds like a bit of a bodge job Ant, and he wants you to run a new larger supply from the Main C/U to feed the Garage C/U again is that correct? what is intended to be fed from the newly supplied Garage C/U?
The circuits are existing in the garage c.u.are 2 x 16A mcb's feeding sockets in the conservatory and outside sockets (rcd protected).A spur of a spur feeding the garage c.u.
 

Reply to New Distribution Circuit to existing consumer unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
704
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
751
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
4K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
869
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock