Discuss New extension to existing wiring in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
2
Just been asked to quote to wire a new kitchen extension. I realise that the new extension must conform to the 18th IEE regs. The existing wiring in the remainder of the building has the sockets lower that the stated 450mm and the light switches are higher than 1200mm. Do these have to be re positioned and rewired?
 
Just been asked to quote to wire a new kitchen extension. I realise that the new extension must conform to the 18th IEE regs. The existing wiring in the remainder of the building has the sockets lower that the stated 450mm and the light switches are higher than 1200mm. Do these have to be re positioned and rewired?
simple answer is NO. as long as your new works comlpy with current regs. e.g. RCDs where needed and confirmation of adequate earthing/bonding.
 
Thanks alban, that's what I was hoping. The owner has recently bought the property and there was no electrical certificate available with the purchase. He would now like to have a test certificate for the complete installation after the extension is finished. Can the installation now be certificated to different standards?:confused:
 
Under regs it is fine as long as the original wiring can carry the new load safely, that it is earthed to current requirements and that the cross bonding is satisfactory. This only takes a few tests, and I expect you would know how.
too serious for this time of nite. even if i agree.
 
Thanks alban, that's what I was hoping. The owner has recently bought the property and there was no electrical certificate available with the purchase. He would now like to have a test certificate for the complete installation after the extension is finished. Can the installation now be certificated to different standards?:confused:
you can firsrt do a EIC for any work you do. then you could do a EICR for thr whole installation.
 
Thanks alban, that's what I was hoping. The owner has recently bought the property and there was no electrical certificate available with the purchase. He would now like to have a test certificate for the complete installation after the extension is finished. Can the installation now be certificated to different standards?:confused:
once you have finished the job and done all the checks on the old and new stuff including eath bonding as barnincks rightly says then that is fine
you should be able to get a certificate from whoever installed it or ask for a reprint from the appropriate person
 

Reply to New extension to existing wiring in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
346
Hi all, I'm wondering if it's permitted to replace an outside wall light myself if I use the existing wiring from the old light. In theory I just...
Replies
2
Views
637
Hi, I’m new to the forum. Thanks for letting me join. Asking for some diy advicd… I’m trying to add a couple more security lights to the existing...
Replies
1
Views
675
Sorry two questions today. We had the kitchen rewired based on existing units, but with a slightly new layout it puts the dishwasher right over...
Replies
1
Views
733
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
Replies
63
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock