Council block of flats
Ryfeild board in ground floor intake (60a bs88 fuse)
flat is directly above intake 2 floors up- but flat fuse board and meter is in middle of flat (not by front door)
Is it ok/ good practise for installing a new supply like the following:
3core 16mm SWA XLPE from Ryfeild (through the 2 floors cleated to the wall in communal area) run approx 10m
Then made off into a metal adaptable box outside the flat front door
using 16mm through crimps covered with heat-shrink
then from this point- 16mm double insulated tails and 16mm G/Y single core in plastic mt4 surface along the hall inside the flat approx 8m run- to the meter and board.
cheers.