Afternoon Ladies & Gents,

I'm a new member to the forum so thought I'd introduce myself.
Been qualified for around 10 years and have finally set up on my own. I am new to the test and inspection side of things so I am seeking advise on the following question. Any help would be greatly appreciated.

A friend of my misses is buying her first property and the seller has had a EICR completed. Now the question is that the installation is recorded as a TN-S with a Ze of 2.1 ohms.

My understanding is that the Ze for a TN-S is 0.8 ohms. Am I missing something or is this reading excessively high?

Any help/advice appreciated

Regards

Clarkie
 
The EICR chaps will be along shortly, in the meantime you are correct that the Ze for a TN-S system is around the 0.8 figure, although in may be higher in rural areas.

Perhaps the home owner should ask the DNO for advice on this matter. They may say it is what it is, and are not obliged to improve it. What did the EICR suggest?
 
This is an interesting question no doubt..... The EICR forms allow you to comment on the incoming service supply but they are technically outside the scope of the EICR.

I would have commented.

Such a high Ze would mean all 20a and above circuits would exceed their max Zs so there must be RCD's installed.

Calling the DNO may result in them not doing anything.....
 
Will upload the EICR later on, but in answer to Midwest yes they did a Zs on both final rings with the same reading of 0.39 ohms

The property must have some chunky metal service pipes in, or the Ze is incorrect. What do ya think EICR warriors?

Have you considered contacting the DNO and asking them, they won't bite and usually will come and have a butchers for free.
 
Assuming the Ze was measured with the main protective bonds disconnected that is far too high and with those Zs readings it sounds like it is being earthed by other means.
 
or the Ze is 0.21 after the tester went to specsavers. i.ve frequently come across TN-S at well under o.8. at home it's 0.18.
 
Something in the information does seem a little strange. If the supply EFLI is that much though then as stated on the Condition Report guidance for recipients:

Where inadequacies in distributor's equipment are encountered, it is recommended that the person ordering the report informs the appropriate authority.

But naturally, it is up to the skilled person to identify the inadequacy and provide accurate information for the person ordering the report to actually report it.

But I very much doubt those readings are accurate.
 
only just got in after an investigation into paul's post regarding his security lights.
 

Reply to New Member with an EICR question on max Ze reading in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
889
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock