Hi,

I've recently run 4mm 4 core SWA from a 20A MCB house consumer unit to a garage unit installed in a shed 50M away. The garage unit has 16A and 6A breakers protected by 40A 30mA RCD main switch. All wiring connections seem to be correct, however, as soon as anything is placed under load either from socket or light, the RCD back at the house consumer unit trips. I have visually inspected everthing so far and cannot see any problems.

I looked for neutral problems and cannot see anything amiss.

Can anyone suggest where the problem maybe?

Thanks
 
I would imagine, that the RCD tripping indicates there is a fault.
It could conceivably be due to an accumulation of earth leakage from a number of circuits being protected by the RCD at the house.
Have you tried switching off the other circuits and then switching on a load in the shed?
 
Most common thing i find with shed installs is water getting into the fittings somewhere, we've had a lot of rain recently and if its just started happening - this is where, if i were you, id probably start looking first.

Spiderman onto the shed roof and see if the felt / tiles (whatever it is) are knocking on death's door.

As above, IR test.
 
I've seen it numerous times. Everything seems fine - IR all circuits, all +100m, then only when you connect a load the supply RCD trips.
As the neutral current is not returned to the sub circuit RCD it throws it out of balance and trips.
 
I've seen it numerous times. Everything seems fine - IR all circuits, all +100m, then only when you connect a load the supply RCD trips.
As the neutral current is not returned to the sub circuit RCD it throws it out of balance and trips.
I know all this but we can say that is definitely the problem here
 
As the RCD will constantly monitor P-E and N-E faults in no load conditions I would say it's highly likely to be a wrongly connected supply neutral but you are right, there maybe circumstances where it could be something else.

Solgen any chance of a picture of the CCU?
 
The other circumstances where this would occur would be that there is, by chance, faults on all loads connected - but why isn't the local RCD tripping! Is it less sensitive than the house CCU RCD - could be!

I'll stick with wrong neutral bar.
 
Hi,

I've recently run 4mm 4 core SWA from a 20A MCB house consumer unit to a garage unit installed in a shed 50M away. The garage unit has 16A and 6A breakers protected by 40A 30mA RCD main switch. All wiring connections seem to be correct, however, as soon as anything is placed under load either from socket or light, the RCD back at the house consumer unit trips. I have visually inspected everthing so far and cannot see any problems.

I looked for neutral problems and cannot see anything amiss.

Can anyone suggest where the problem maybe?

Thanks

Yup. you need to post more info mate.
 
This is the electricians forum, how the hell are we supposed to know whats going on here?

if i were the OP id take it to the plumbers forum.

They know best.
 
Ive got a similar issue with a customer. Although i have not done any tests yet as i popped in when passing. 40amp mcb in the cu not on rcd. 4mm Swa to summer house in garden. 40amp rcd as main switch in summer house.
The RCD trips on every circuit when load is required. But is fine when all mcb's are off, Now it was working fine up until a couple of months ago when it stopped.
So im going back when they return from their hols in 4 weeks or so im thinking the swa has failed ir or faulty rcd.
 

Reply to New shed circuit tripping RCD at house consumer unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a fairly recently installed consumer unit with an RCD, between it and the garden there is another, much older (25yrs?) RCB (big Wylex...
Replies
11
Views
2K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
877
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
714
I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
Replies
55
Views
4K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock