S

sparkyork

hi everyone, just been too look at a nice job in leeds which should give me plenty of work :)
shop is approx 15m x 35m ish with a mezanine floor at one end.

couple of questions as ive done a bit bit not that much comemrcial stuff.

1. there are going to be a max of 12 refrigerators, do i split this into 3 or 4 circuits or....?

2. 4 air conditioners, thinking of suppliying these seperately
3. small cafe area to the back of the shop, with 3 phase cooker. and a seperate socket circuit just for this area, aswell as its own lighting circuit.
4. thinkin of keeping mezanine sockets and lighting on there own circuits.
5. office with computer on its own socket circuit.
6. tills on there own circuit

that ll do for now, guess you get the idea'ish! dont know what lighting but theres gonna be a lot of it, so im allowing 6 circuits for this. as well as e/lighting circuit.
thinking of using a 36way 3 phase board and after counting circuits so far (not all mentioned here) ive got 29 ways so...

also, down the sides of the shop is wooden display units incorporating the refrigerators etc going all the way down to the bottom. fridges gonna plug in above these units and be out of sight via a pelmet. im thinking of running 2x4" trays down either side of the shop just obove these units and was wondering what the best way of terminating into socket outlets would be? dont wanna run swa everywhere as its all out of sight and in no danger so wanna use standard pvc, (peel off the tray into metal clad sockets/via grommets or...)

also the lighting is gonna run on these trays as well then peel off upwards into conduit going up the wall and across to relevant "clix" outlets for the lighting, again wanna do this in pvc.

your comments suggestions are greatly appreciated

rich
 
cant immediately fault any of the above although im sure someone can give you further advice ,looks like your'e going to be busy
 
Not trying to teach granny to suck eggs but check on the 'fridges' going down the wall. Some suppliers are now providing units with air con like external units needing an external isolator and they specify the internal connection must be via a BS4343 SP&N interlocked socket. :cool:
 
yeah looks like im gonna busy for a while!! ill get some pics up of it at the minute, just one big empty concrete box!

good point that tony, ive spoke to customer tonight and ive already asked for the rating of the fridges, so when he gets back to me i can confirm what you mentioned. again it kinda begs the question..if ive got a tray running horizontally down the wall is it gonna be ok running it all in standard T &E and possibly terminating these cables into an isolator then onto bs4343 socket? to be fair im more used to terminating swa into these accesories, but cant see the point in using this when its all out of harms way etc

rich
 
Not trying to teach granny to suck eggs but check on the 'fridges' going down the wall. Some suppliers are now providing units with air con like external units needing an external isolator and they specify the internal connection must be via a BS4343 SP&N interlocked socket. :cool:


Tony is correct was going to say the same ! Also the air cons I have done have been three phase and I have just used an Isolator.
 
hi rich, i currently do quite alot of scotmid shops over scotland ie little "coop shops " with the same ideas we have a seperate board for refridgerators as normally they have this board next to refridgerator control panels and also take up quite alot of room and good i suppose to keep lighting and power in one board also being sub mains seperate earths run to each board , also we put small 10 way board into office with computers i suppose to stop people turning off by mistake,also tills we run 4mm radial clean supplies coming down to tills in chrome poles if coming over ceilings along with a ring main if other sockets are require over others tills for cleaners or any other day to day use, lights: a key switch at front door or however they get in, lighting up a passage to bank of switches for shop or switch with contactors ,refridgerators same idea as above each unit but hidden under pelmets and using either 16a 240 3 pin sockets or 32a 415 5pin sockets depends on size of them i suppose we feed these seperate in swa's all going back to boards on tray, Air cons spurs we put a couple of rings for them . theyve started getting us to extract from above where the bake the bread out onto shop floor as they think customers smelling this helps sell bread etc haha.. lighting through shop we normally use 150w hqi fittings metal halides" jcc made " straight down on shop floors and up aisles and tilting on permiter onto fridges . hope this has helped mate in any way .. heres a pictures of kinda the same fittings (HQI-TS DL150 Downlight) or (HQI-TS DL70 Downlight) 70 w version also used these but would recommend the 150w
 
Last edited by a moderator:
cheers lee really appreciate the input, gonna be speaking to customer 2moro now as its a bit late now. will find out whats going on with the fridges and air con setup, have to agree jcc do some pretty nice fittings as well, infact the customer was in manchester when i last spoke to him seeing about getting the manufacturer to come up with a lighting plan (i was never any good at all the formulae attached to working out height of fittings appossed to lumenicity and all that! lol)

is there anything wrong with using t & e for the supplies for stuff? what conditions generally have to be in place that recommend the use of armoureds? ps dont know if i mentioned but theres gonna be about 12 fridges

cheers everyone

rich
 
if single phase and out of reach for joe public no dont see why not but if three phase then swa. we also had to wire all t+e in low smoke cable the white ****e thats impossible to strip haha might want to find out as for all shops and council stuff thats what they ask for .
 
Last edited by a moderator:
yeah cool lee, will get some more info 2moro, obviously its early days yet but theres just so much to think about!!
also dont think we'll be going for having seperate consumer units either. dont know whether to rely on the customer to get the info from the council as he's a bit forgetful, might sort that me self in the morning.

forgot to mention....theres a metered supply terminated into a sw/isolator in the commercial unit. customer informs me its a 45kva supply i didnt get chance to have a right good look as i had no steps with me and it was to dark. in peoples experiance and due to.. 45000/400=112.5A and 45000/230=195.6A can i expect it definately to be a 3 phase supply? will find out for definate 2moro but i just need to know now!!
 
Last edited:
Know what you mean about lighting formulae and design but I found Illuma do a free CD with lighting design facilities. It's quite easy to use after a bit of practice and if you are using "standard" fittings you can substitute other manufacturers equivalents when the design is done.:D
 
well top marks to those of you that mentioned the 16a bs4343 (commandos)!!

thats exactly what the guy supplying the fridges has said he needs :)
im hoping to get some gear ordered by tommorrow night so i can start next week. ive asked him to find out the rating of these fridges, is it generally common practice to supply these 4343's with individual radials or.... (suggestions please!!)

he's also got an air con bloke he's seeing tommorow, theres gonna be 4 units alltogether, the bloke supplying them also told him that 3 phase conditioners are more efficient that single phase ones. he asked if this was true? i said i would pressume so as i know 3 phase motors are efficient but again im not 100% on this either.

also been doing a bit of reading in the big red book, im struggling to find formulae for working out cable grouping on a horizontal perferated tray, it states in there that mixing different sized/currents etc can be iffy and that its out of scope of it all?

im thinking of a 6" tray that'll have some lighting feeds on it, power feeds for fridges, till, and thats about it. so long as i keep lighting on one side of tray and power at other and try and maintain a descent gap between it be ok wont it? gonna be a seperate smaller tray for low voltage stuff as well

knows its a long message but ive got a lot on me mind! lol

cheers
 
I had a couple of these beasts to install last year. The manufacturer/supplier actually specified individual radial circuits with the interlocked sockets. Whilst they run quite efficiently there is quite a pull on start up. Also, as far as your customer is concerned, a fault occuring on one while the shop is closed will only result in that specific unit "going off" if it trips the breaker, so the majority of the stock is not adversely affected. Remember to check if there an external unit with the fridges. This job is going to keep you active for a while. Nice one.:)
 
cheers matey from what i can gather he had the option of getting external coolers for the fridges but didnt having planning permission for it so isnt bothering.

at the start of your post are you talking about air con or refridgerators?

yeah i agree its gotta be wise running the fridges on seperate radials, what would you use swa, or nice chunky flex? also you can get hold of combined isolating 4343 outlets are these gonna be acceptable?
 
Have you thought about using SY, you're using it internally and it's nice and easy to get round your tray. Also will go into 4343's neatly.
Interlocked 4343 sockets are readily available with theplug being mechanically locked in when the integral isolator is switched on. strange as it may sound Gewiss do a good little unit for SP&N 16amp.
It was the fridges I had to install the supplies for but the shop also has air con fitted at the same time so had that to do aswell.:cool:
 
yeah thought about it but didnt think about it enough, makes sense i suppose, ill get a price from wholesaler in the morning for a drum of it. think im gonna supply each fridge seperately
 
hi all, had me 1st day on the job today, got a bit of tray on the wall, took me a while to get back into the swing of things! ill get some pics uploaded 2moro.

customer didnt like my ÂŁ1.29 per metre price tag for sy, and didnt want swa either. so im doing it in T&E, pealing off the tray down a small amount of conduit into the commandos.

checked the supply at the back of the unit and its dead so he needs to get his landlord to do something about that! theres defo 3 phases there aswell. its a 4 core 25mm swa, but im a little concerned theres no seperate earth ran with it. should i recommend my customer asks for this to be instated? i know you can use the armouring but i dont like it not one bit! also the isolator says 63a in the bottom right corner, im presuming this means 63a per phase capacity? hopefully get in the meter room 2moro and really see whats going on.
 
swa as earth is ok BUT IT NEEDS CALCULATING we did a job and had to run a seperate earth after calcs 25mm over 50m.
also bonding needs taking account of ......again someone else can give better advice
 
yeah i just dont trust it, i like to see a nice big seperate earth. its only gonna be 10-15m run at the very most, there is a water supply coming into the unit so im gonna stick a bond on that as well. as well as a supp bond to me cable tray? gonna do some reading tongight on rcd's in commercials or is it simply gonna be rcbo's on everything as there will be no cables below 50mm etc?
 

Reply to new shop in leeds in the Electrical Forum Canada area at ElectriciansForums.net

Similar Threads

Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi Everyone, I'm new to this forum and am hoping someone can give me some advice, as I'm absolutely clueless when it comes to these things. I'm...
Replies
11
Views
2K
Hello, I am renovating a house. I am rewiring myself. I am getting an electrician to install a new consumer unit & test all my work. I'm looking...
Replies
20
Views
3K
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock