Discuss New smart meter, storage heaters now trip RCD in the UK Electrical Forum area at ElectriciansForums.net

Brian N

DIY
Reaction score
9
I have just had a "smart" meter installed , and at night the electrics trips the RCD when the night storage radiator section comes on. I have had them out and they said installation was correct. I know a little about electrics (more over cautious and basic) but was suppressed when I looked at the lay out for the Night storage CU that the neutral goes through the RCD but the live goes direct - could this be a cause for the RCD to be triggered. I will have to get an electrician out to check all the wiring for the storage heaters if I cannot persuade them they have done something to suddenly make my electrics trip when that CU is on. Everything else seems to work fine. I have attached a simplified circuit diagram - electrics in the house have always been a little spaghetti junction, but never had any problems. Local electrician has always installed new stuff properly. Can anyone help? or suggest what my problem could be.

If I turn the CU for the night storage radiators off - then I get electrics 24/7 - if I turn that batch on then it pops overnight.
 

Attachments

  • IMG_7575.JPG
    229.7 KB · Views: 81
  • IMG_7576.JPG
    434.1 KB · Views: 74
  • IMG_7577.JPG
    310.8 KB · Views: 71
  • IMG_7578.JPG
    410.1 KB · Views: 65
  • IMG_7579.JPG
    366.5 KB · Views: 71
Hi. If your diagram is right, and i have to say it looks to be, then I agree that isn’t going to work.
As you said the N split is the wrong side of the RCD (which is acting as fault production for the older consumer unit which has no RCD and you probably have an Earth rod - a TT setup).

My guess is that the henley block under the rcd was originally used to split the Neutral. It’s now used pointlessly to split a Live.
I’d try calling them again.
They have certainly messed up in my opinion but it might be quicker to get a sparks to fix it as the issues are all downstream of the meter tails. Then write a letter of complaint!
 
Hi. If your diagram is right, and i have to say it looks to be, then I agree that isn’t going to work.
As you said the N split is the wrong side of the RCD (which is acting as fault production for the older consumer unit which has no RCD and you probably have an Earth rod - a TT setup).

My guess is that the henley block under the rcd was originally used to split the Neutral. It’s now used pointlessly to split a Live.
I’d try calling them again.
They have certainly messed up in my opinion but it might be quicker to get a sparks to fix it as the issues are all downstream of the meter tails. Then write a letter of complaint!
Thank you, as I said my basic knowledge of electrics - and gazing at it - I think the people who install, and the person who came out to look at it are not electricians - more installers - if that make sense.
 
Thank you, as I said my basic knowledge of electrics - and gazing at it - I think the people who install, and the person who came out to look at it are not electricians - more installers - if that make sense.
Meter Monkey is a more accurate title.
 
An rcd works by sensing an imbalance on the current on the live and neutral. If the difference is over the threshold of, I would presume, 30mA, the rcd trips…. As far as it knows, the spare amps are going to earth, and it’s doing what it’s meant to.

when your off peak comes on, whatever load on the live is not detected at all by the rcd, but the neutral is…. As it should be balanced, it’s tripping out.

Are you using any off peak heating just now? It might be worth testing by turning the off peak board off completely and seeing if the rcd holds as no load at all will be going through.
 
An rcd works by sensing an imbalance on the current on the live and neutral. If the difference is over the threshold of, I would presume, 30mA, the rcd trips…. As far as it knows, the spare amps are going to earth, and it’s doing what it’s meant to.

when your off peak comes on, whatever load on the live is not detected at all by the rcd, but the neutral is…. As it should be balanced, it’s tripping out.

Are you using any off peak heating just now? It might be worth testing by turning the off peak board off completely and seeing if the rcd holds as no load at all will be going through.
If I turn all CU for the night storage radiators off I get uninterrupted power for the rest of the house - only issue is if I leave the storage heater bit on - it then trips when the power to that bit kicks in. Your comments confirm my suspicion that sending the neutral through the RCD and the live direct is causing the problem.
 
Thank you all for your replies, I have contacted the meter installer lot, hopefully they can rewire the bit where they made the error. I expect they are not used to installing in an old property with old mechanical meters, three CU, one of which is for night storage radiators. I did jokingly ask if they could send an electrician this time, and they did say they did not have any of them, just installers. You would have thought they could have some trouble shooting electricians to help out.
 
Thank you all for your replies, I have contacted the meter installer lot, hopefully they can rewire the bit where they made the error. I expect they are not used to installing in an old property with old mechanical meters, three CU, one of which is for night storage radiators. I did jokingly ask if they could send an electrician this time, and they did say they did not have any of them, just installers. You would have thought they could have some trouble shooting electricians to help out.
Great, it isn't in fact too complicated to sort.
It just needs a henley block in the N from the cut-out BEFORE the RCD, then the N to the off peak CU removed from the top henley block, shortened and put in the new henley block.

(Though if they are pulling the fuse, they may prefer to run a new off-peak tail and re-purpose the block underneath that's there)
Up to them anyway!
 
These not so smart smart meter installers clearly are not trained to install on anything but the simple jobs and also work to the if you don't know ask principle
I wonder how many smart meters are actually installed where there are issues with the DNO equipment like main earths missing that are never addressed, the installation of smart meters would have been a good opportunity to get an overall assessment of the state of the installed distribution throughout the UK but the quality of the installers means it isn't going to happen
 
Great, it isn't in fact too complicated to sort.
It just needs a henley block in the N from the cut-out BEFORE the RCD, then the N to the off peak CU removed from the top henley block, shortened and put in the new henley block.

(Though if they are pulling the fuse, they may prefer to run a new off-peak tail and re-purpose the block underneath that's there)
Up to them anyway!
I think I can see a slightly old TN-S setup under the main head, in which case this is the way to do it.

It's just possible that you are on a TT (earth Rod) - in which case you may need a functioning RCD on the storage heater circuits too to ensure fault protection is working. Alternatively it may be possible to get the DNO for your area to upgrade the earthing to PME.

It may be worth getting an electrician to check things over generally - it may be sensible at some point in the not too distant future to look at updating things a little, especially if you are likely to be doing any electrical work in the future....

Nothing wrong with what you have at the minute, assuming that the RCD is tested regularly with the test button. Just that it is probably >40 years old at this point.
 
These not so smart smart meter installers clearly are not trained to install on anything but the simple jobs and also work to the if you don't know ask principle
I wonder how many smart meters are actually installed where there are issues with the DNO equipment like main earths missing that are never addressed, the installation of smart meters would have been a good opportunity to get an overall assessment of the state of the installed distribution throughout the UK but the quality of the installers means it isn't going to happen
They will admit it themselves when I've talked to them - they have a plug in socket tester and a non contact voltage tester for verifying polarity - that's it...

I agree that it would have been a great way for the DNOs to update their records to actually comply with their legal requirement to provide the details of fusing and earthing on request...
 
Taking another look at the pictures if the meter tails were taken from the RCD and connected into the henley blocks above the CU and the CU tails taken from the henley's and connected to the RCD that would be a better fix as the CU to the right already has an RCD in it
 
I think I can see a slightly old TN-S setup under the main head, in which case this is the way to do it.

It's just possible that you are on a TT (earth Rod) - in which case you may need a functioning RCD on the storage heater circuits too to ensure fault protection is working. Alternatively it may be possible to get the DNO for your area to upgrade the earthing to PME.

It may be worth getting an electrician to check things over generally - it may be sensible at some point in the not too distant future to look at updating things a little, especially if you are likely to be doing any electrical work in the future....

Nothing wrong with what you have at the minute, assuming that the RCD is tested regularly with the test button. Just that it is probably >40 years old at this point.
Very sensible comments, I ought to get someone in to take a fresh look at the setup at some point, although the installation of a smart meter has not helped. The original unit was looking old when we moved in some 30 years ago! We do have an earth rod, massive thing stuck into the ground. The other thing I did not mention was the "smart" meter does not work as it will not connect to their network (is it mobile phone?) so all this fuss and it is not reporting back to base - expect I will have to read this meter somehow for them!
 
Very sensible comments, I ought to get someone in to take a fresh look at the setup at some point, although the installation of a smart meter has not helped. The original unit was looking old when we moved in some 30 years ago! We do have an earth rod, massive thing stuck into the ground. The other thing I did not mention was the "smart" meter does not work as it will not connect to their network (is it mobile phone?) so all this fuss and it is not reporting back to base - expect I will have to read this meter somehow for them!
So a not very-smart-meter, installed by a not-very-smart installer - excellent!

The earth rod may not be providing the only earth, but if it is, you may well need RCD protection on the storage heaters - or need to get the earthing upgraded by the DNO (who will sometimes do so for free).

It can be tested easily enough by someone with the right meter - may be worth finding a decent local electrician to just have a quick look over things - won't take very long to get a good idea of the installation and whether it's an issue or not...

But the meter installer should be coming back to resolve the issue they caused in this case anyway...
 
It's funny how when working off photos you can have all the right questions and get the answers totally wrong....
I was thinking "Is it TT, and do you need an RCD for the off-peak CU". Yet managed to miss the (likely) TNS connection and thought the off-peak CU had an RCD because there's a similar CU in a picture which does have an RCD.....
I'm glad other people were on the ball!
 
It's funny how when working off photos you can have all the right questions and get the answers totally wrong....
I was thinking "Is it TT, and do you need an RCD for the off-peak CU". Yet managed to miss the (likely) TNS connection and thought the off-peak CU had an RCD because there's a similar CU in a picture which does have an RCD.....
I'm glad other people were on the ball!
So does the live that goes to the storage heater CU need to go through the RCD - so instead or removing the neutral from going through the RCD - send both live and neutral through the RCD? I can see I need to get an electrician out after the meter installing team have finished.
 
So does the live that goes to the storage heater CU need to go through the RCD - so instead or removing the neutral from going through the RCD - send both live and neutral through the RCD? I can see I need to get an electrician out after the meter installing team have finished.
Oh dear I've confused things even more....sorry....
1 - main things is that it has to work again, and splitting the N before the RCD is almost certainly how it was before, and this is how I'd put it back. Alternatively the L could be moved to other side of RCD. That works too.
2 - There's a secondary question of the earthing arrangements, if it's what we all think it is and what it looks like, there is no issue, and lack of RCD protection for storage heater CU is not the end of the world, just something that's advisable these days.
If on the other hand the earthing is really all from from the earth electrode then the lack of RCD protection would be a considerably bigger deal from a safety point of view.

I hope that clarifies things a bit! Basically let the meter people make it work again, and then best to get someone to check it over.
 

Reply to New smart meter, storage heaters now trip RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day readers, if any,I am an old sparky, a very old sparky. I can remember old Faraday giving us lectures Wednesday evenings at evening...
Replies
1
Views
395
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
558
Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
766
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
863

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock