Hi,

House I am working on s having a new sp & n supply installed. As a result the new incomer will be approx. 15 meters away, so I need to run a sub main.
Main fuse is 100A so was thinking of putting an 80 amp sub main with 25mm 3 core swa. But got me thinking Is this over kill ad would a 60A sub main with 16mm 3 core swa suffice.
Usual loads of shower 9kw, cooker, micro oven and elec hob, utility room. Normal lighting and socket layout.
Calcs for diversity over 60A, but experience says 60A should be ok.

Customer is running a tight budget as usual!

What do you guy think, 16mm 60A sub main or 25mm 80A?
 
New supply due to fault on existing, relocation of main head due to new extension being in way, and 15 meters is around part of the house!
 
Is there much difference between 16mm and 25mm SWA? £2.50 per meter maybe - so for a difference of about £40.00 I'd recommend the 25mm

If they can afford a big extension, then about £40.00 isn't even a drop in the ocean!
 
I'm with Murdock on this one. For what its worth, go with the 80A.
 

Reply to New Supply! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I currently on a job where the garage is having an office built above it with solar panels installed on the roof. I have ran a 16mm 3 core...
Replies
3
Views
142
190m run SWA underground, supplied from 3p+N 240mm sub main, each cabin total demand is 80A, worked out 35mm but volt drop is about 8%, would this...
Replies
9
Views
714
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Replies
10
Views
510
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
798

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock