Had to help a a colleague who has all the qualifications but no clue to anything. Lol
I've recently completed my level 2&3 and 18th Editon.
Doing a EICR, Two ring finals with no Earth continuity, found the break on the CPC the downstairs ring, the other is a 32A ring final just for a Boiler ?????? We cant find the break on r2.
Is it possible to downsize the MCB to a 20A and change it to a Radial,
That's what i suggested and he said no, wants to smash up the customers house to rectify the break.... confused.com
Much appreciated. Jimbo