Thanks for all your advice, positive and negative.
We have all got to start somewhere, this is a new career for me and wanted the help of experts to get a good start.
For your information I chose this system because the previous one was unsafe and needed replacing badly.
 
when you are using RCD s for fault protection, as in this case , the max. Zs values are obtained from table 41.5, BGB. but, i'd still try and reduce the Ra. when eng54 breads this thread he'll tell you that you should be able to attain a sub-1 ohm value with some effort. LOL.
 
Thanks for all your advice, positive and negative.
We have all got to start somewhere, this is a new career for me and wanted the help of experts ly.
to get a good start.
For your information I chose this system because the previous one was unsafe and needed replacing badly.[/QUOTE]

surely replace it goodly. looking at your layout of circuits, i can't find fault there. good division of circuits. be an idea if you could post the r1,rN & r2 readings for the 2 rings as well.
 
Would be a good idea to replace the 100a main switch on your CU for a 100a 100ma S type RCD main switch. Currently you are dependant on the 30ma RCD's for earth fault protection,a 100ma main switch gives back up if they fail to operate. That said the CU layout and Ze value you have complies with the regs for a TT earthing system.
 
Would be a good idea to replace the 100a main switch on your CU for a 100a 100ma S type RCD main switch. Currently you are dependant on the 30ma RCD's for earth fault protection,a 100ma main switch gives back up if they fail to operate. That said the CU layout and Ze value you have complies with the regs for a TT earthing system.


Here we go with devils advocate

the above will help for sure but 100mA time delayed is not a life saver necessarily....why not just bung another 30mA RCD in series? Especially as they're 90% of the time all within a few inches of each other.... Isn't that "safer"?

apart from tripping over on the way to the fusebox becuase its snowing,dark,no candles, no torch, ........
 
the 100mA RCD would be a back up fault protection device, not additional protection. for that you are relying on the 30mA devices.
 
Are you accidentally pressing the button to test continuity....if you are you are nulling the leads to 0

I did exactly that with my 1730 recently, getting 0ohmms on continuity readings, really does throw you! I rang Megger technical thinking my tester had gone u/s. Really helpful person talked through problem, and you can 'over null' you tester. As the Megger 17 series will 'remember' your leads, it's a good idea just to test them each time you use them, or reset & null them. I still forget now.
 

Reply to Newly Fitted 17th Edition Consumer Unit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
1K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
762
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
I was just googling for skeleton boards after reading the last thread and various pictures of consumer units popped up, some wired terribly and...
Replies
6
Views
735
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
757

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock