A Question i have newly installed a Radial citcuit for a shower i have used a 10mm t&E cable about a 20 metre run when completing the continuity test of cpc i a m receiving a 0.21 Ohms reading the metrel tester i am using is showing up a red X on the display screen any ideas ?
 
I would say that's a bit high. Based on the figures in GN3 for resistance of a 4mm core (I'm assuming it's a 4mm cpc), I get around 0.09 (4.61mOhms/m x 20). As for the red X, never used a Metrel, time for the user manual I think.
 
Is this a test of R2 or R1+R2 ? tabulated values for R1+R2 for 10mm/4mm t&e should be about 0.13 at 20m.
High resistance connections, anomolies in test leads, low batteries in tester etc could all be contributing to a high reading.
 
A Question i have newly installed a Radial citcuit for a shower i have used a 10mm t&E cable about a 20 metre run when completing the continuity test of cpc i a m receiving a 0.21 Ohms reading the metrel tester i am using is showing up a red X on the display screen any ideas ?

First check the manual to find out what the red X means, you should reject the measurement until you have got past this potential issue with the equipment.
Have you nulled the leads correctly? Did you have good contact pressure on the probes?
Did you consider the accuracy of the tester?
Are the batteries in the tester fresh?
 
Have looked at the metre still having issues with the red x on display it is a test of r1+r2 charged up batteries this morn still having issues tho.

Well in that case, if it's R1+R2 for a 10/4 T+E, it's 6.44mOhms/m according to GN3 and you should be expecting something in the region of 0.13ohms.

Having just had a quick skim of a Metrel manual (for the EuroTestXC), a big red X implies the test results are outside of a configured acceptable range. If it's 'Cal X', then the lead resistance hasn't been compensated for.
 
Need to spk with someone i re did the shower r1 r2 test got 0.01 ohms to begin with and got a green X then trying it again i jave gone straight bk to a red X wracking my brains on this one very strange have nulled the leads but getting very mad results lol
 
As been advised, check connections, check batteries. Unless the testers u/s, you should get the same (or very similar) test results.

Plus not knowing the meter (but think I understand the concept), 0.01 ohms gets a green X pass but the readings too low and 0.21 ohms gets a red X, fail on both counts. :)
 
With metrel you can set a fail level for continuity. On mine it's default is 2 ohms. Often get a red X when testing continuity of long lighting runs but that's just because I can't be bothered to adjust the limit. I don't look at the X, it's meaningless so long as you know what figures you should be looking for
 

Reply to Newly Qualified to domestic level in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, Sorry, I won't take much of your time. To cut a long story short, I am newly qualified and have domestic installation/commercial...
Replies
0
Views
431
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
14
Views
474
Hi everyone, I'm currently working towards getting qualified as an electrician and am hoping to get my foot in the door with an apprenticeship or...
Replies
0
Views
935
Hi to everyone, this is my first post so if is been already asked/answered please guide me to the relevant discussion/thread. I don't know...
Replies
6
Views
447
Hi guys & gals, I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday...
Replies
10
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock