Discuss Nightmare of a day. RCD tripiing under any load in the UK Electrical Forum area at ElectriciansForums.net

What's confusing me is why when I plug anything into kitchen socket covered by RCD A is it tripping RCD B? Surely this means it can't be a N to E fault as it would trip RCD B if this was the case

If you have an NE fault on a circuit on one RCD then loading a circuit on the other RCD can cause the first RCD to trip.
Did a diagram for you:
RCD Trip due to other side loading.jpg
 
Every time we get a thread about RCD's tripping after a CU change, the common consensus is either a N-E fault or a shared/borrowed neutral. And every single time the OP has failed to test the installation prior to replacing the old rewirable CU with one containing at least two RCD's.

How many more times do these guy's NEED to be told to test these installations before they start changing them out for god's sake??

What's more, why is this fault causing such a problem to find and rectify. I would have thought that in around an hour, an experienced electrician would have sorted this problem out, ...or at the very least well on his way to finishing off any remedial work...
 
Eng54 do you honestly think in the real world customers would give the go ahead to carry out testing before changing a board? This would mean an additional cost on top of a board change The customer would simply get someone else to do the job!
 
A test for borrowed neutrals plus an IR plus an EFLI wouldn't take very long at all would it?
You've already done enough there to identify any major problems and you're doing the rest of the tests anyway on completion of the change so what's the problem?
 
Eng54 do you honestly think in the real world customers would give the go ahead to carry out testing before changing a board? This would mean an additional cost on top of a board change The customer would simply get someone else to do the job!

Its not an additional cost. Its part of the cost of doing the job right from the start. Not every customer wants it cheap, most want it done once and done right.
 
The problem you know have is a potentially peed off client,did you leave them without power last night? And possibly a lot more work to do if it's not a quick fix,if you test thoroughly before swapping the board any issues will be found and corrective action and any further costs can be discussed with client.
 
Eng54 do you honestly think in the real world customers would give the go ahead to carry out testing before changing a board? This would mean an additional cost on top of a board change The customer would simply get someone else to do the job!

What do you mean extra cost?? The Minimal IR/ELI/Shared Neutral tests are for ''YOUR'' benefit, so that you know, or are aware of any problems, (such as you have now) before you start!! Armed with that information, you can advise your customer of any extra costs that will be associated with the board change!!
 
Eng54 do you honestly think in the real world customers would give the go ahead to carry out testing before changing a board? This would mean an additional cost on top of a board change The customer would simply get someone else to do the job!
what a bunch of old twaddle this is...

having read all this its clear to me you are not competant to carry out board changes....

leave such stuff alone until you have gained the necessary experience
 
Brizo, no disrespect but you may need to shadow a more experienced spark, if not to improve your knowledge, them to learn the correct proceedure and why it's correct.
Are you fresh out of training?
 
Eng54 do you honestly think in the real world customers would give the go ahead to carry out testing before changing a board? This would mean an additional cost on top of a board change The customer would simply get someone else to do the job!

When you have completed the CU install, you will have a completed test sheet with the test data for each circuit (I hope), so you can just as well do some of that testing before doing anything to the old board, just in case it throws up things like N-E faults, or broken rings etc. There is minimal extra cost, but potentially saving a lot of embarrassment.
 
Eng54 do you honestly think in the real world customers would give the go ahead to carry out testing before changing a board? This would mean an additional cost on top of a board change The customer would simply get someone else to do the job!

I have to agree with Eng here. Basic tests at the time of quoting take 20 mins tops, and save a world of pain down the line. Also, the added bonus of carrying out a few basic tests gives you time to chat to the client and show them your shiney MFT. They get to know you, see that you are competent, and will usually give you the go-ahead there and then. Much better than someone who pops in for 2 minutes, gives a rough quote, then adds to the bill later on when the issues raise their ugly head.
 
I know it's like an echo now but I agree with the above comments, testing should be done before you change the DB. I wouldn't change one without testing otherwise it just comes back to bite you like this. Then the customer rolls the old "well it was fine before".
 
I know it's like an echo now but I agree with the above comments, testing should be done before you change the DB. I wouldn't change one without testing otherwise it just comes back to bite you like this. Then the customer rolls the old "well it was fine before".

Same as this. If they have had a quote off another "sparks" who's cheaper because he is going to lash it on and hope for the best, then let em do it. You may well get the call when it goes ---- up :smug:
 

Reply to Nightmare of a day. RCD tripiing under any load in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
342
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
580
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock