Discuss Nightmare of a day. RCD tripiing under any load in the UK Electrical Forum area at ElectriciansForums.net

You say your not a Electrical Trainee and have done 2391 so my question is what the hell are you doing energizing a replacement consumer unit when clearly you have not undertaken any testing! Sorry but clearly you should go back to college!

With regards to no time to test prior I always always book a 5 minuet slot in at the end of a day prior to starting the replacement CU usually on way home from a job to do 2 IR Tests!
1. IR - LE
2. IR - NE

This takes about 5 minuets to do and will never put you into this situation where you have a not tested CU which you have energized and "TRIP"


so you telling me you learnt everything in college? i think i know the answer to that mate
 
Ok so if you have a customer half an hour away you will travel there at the end of a day grafting to carry out a few tests then go there the next day? You obviously have more time than me. Well sorry mate but that's not for me and I can guarantee you 99% of sparks wouldn't do this either!

With regards to energising the board prior to testing. In a newly wired job I would not do this but because it was a straight replacement I will admit I do this and again so will the vast majority of other sparks

What a load of HOT AIR!

Yes I have had some CU Changes some 3 hours away and every time if its not practical I always IR before undoing anything!
You dont need to unplug anything anything as at the end of the day your only "PAT Testing" the appliances and installation all at the same time!

This is an added bonus because if an appliance has a fault then you can quickly identify this before starting.
I did this the other week - Dead short NE and <1Mohm LN and LE. Advised them it needed fault finding at rate which they agreed to - spent 4 hours and over 50% of cables where shot! went from CU Change to rewire like that!
 
so you telling me you learnt everything in college? i think i know the answer to that mate

Not at all - just clear basics - dont energize circuit unless you tested it!
Common Sense sorry

To brizospark

Forget the IRs for a minuet as that will be picked up with the RCD, but what about no continuity on conductors and you have protected 2.5mm broken ring with a 32A!

Sorry cowboy springs to mind - and considering you need to issue a certificate how do you get these results? Disconnect everything again to retest it? Or make up the results?
 
If people are suggesting they have been asked to come in and replace the CU...who is making that decision? The client?
If someone rings me and asks to have a CU replaced I would want to know why they think it needs changing?

As the inspector that is up to me.

If a CU needs replacing there's every chance the wiring will need attention, therefore surely testing has to be carried out?
 
What a load of HOT AIR!

Yes I have had some CU Changes some 3 hours away and every time if its not practical I always IR before undoing anything!
You dont need to unplug anything anything as at the end of the day your only "PAT Testing" the appliances and installation all at the same time!

This is an added bonus because if an appliance has a fault then you can quickly identify this before starting.
I did this the other week - Dead short NE and <1Mohm LN and LE. Advised them it needed fault finding at rate which they agreed to - spent 4 hours and over 50% of cables where shot! went from CU Change to rewire like that!

No wonder the local sparks are complaining!
 
I never test when quoting. I provide a quote for board and explain in simple terms that any faults that are found (if any) will be charged accordingly. Also i agree with some posts that this situation seems very simple, no disrespect to poster but i would have known this fault as a 1st / 2nd year apprentice. Qualifications are one thing but nothing without the experiance.
 
So LED you say you do this for board change three hours away. So you are telling me after a day working you will drive a six hour round trip to do two IR Tests then go back next morning ? WTF? Are you for real? How much are you charging because the fuel cost alone would be ridiculous
 
Solar is right enough what's the point in having this forum if you can't ask!! What do these guys want to just talk about how great they are and how they know absolutely everything!!
 
No it is for electricians to help each other. Not for people who are lazy to carry out work and expect the interweb to help them when the brown stuff hits the fan.

Just out of curiosity will you carry out a global IR on the next DB change that you have to do?
 
So you guys who don't bother testing are happy to give the customer a surprise when the bill doubles at the end of the job?

Yes. Customer is told before that if any problems / faults found they will be charged at £40 ph. This is verbal when quoting and written on quote in black and white. Im not testing on a quote, as far as im concerned if i pick up my tester then im working, and unless the customer would like to pay for a test before then im not doing it.
 

Reply to Nightmare of a day. RCD tripiing under any load in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
349
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
589
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock