Discuss Nightmare of a day. RCD tripiing under any load in the UK Electrical Forum area at ElectriciansForums.net

So you do the bonding continuity, global ir, and i presume ze (possibly one of the most important). Fair play if you do, but i dont unless its being paid for. May aswel do R1 R2 & be done with it lol
 
I would agree that under most conditions that powering up before testing isnt right but on a domestic CU change where there are no circuits added/altered and everything was functional before then like Dr Pepper says the worst that can happen is a tripped RCD, as in this instance, the fault was rectified. This is getting boring now!

Sorry it's boring you but I was originally trying to help, if I new you had been to lazy to do IR tests I would of left you to it,
 
I do the same tell customer we have to do a full test which may add cost, but I include £40 to each quote which is refunded if no faults are found. Works a treat for me
 
I would agree that under most conditions that powering up before testing isnt right but on a domestic CU change where there are no circuits added/altered and everything was functional before then like Dr Pepper says the worst that can happen is a tripped RCD, as in this instance, the fault was rectified. This is getting boring now!

And the worst think that can happen is not checking all the accessories and leaving an exposed live part that you didn't know about and that you are now responsible for
 
I'm still struggling to grasp how an engineer is requested to change a CU without testing? Surely someone must have carried an EICR for the request to be made??
Then, I can't understand how engineers do not submit test certs as standard for a CU change? How can you charge extra for a document which is required by regulations?
 
No EICR is required, most of my CU changes come from the client just wanting to upgrade to an RCD after seeing a campaign in my local paper placed inline with a campaign I'm running along with the ESC about RCDs
 
I'm still struggling to grasp how an engineer is requested to change a CU without testing? Surely someone must have carried an EICR for the request to be made??
Then, I can't understand how engineers do not submit test certs as standard for a CU change? How can you charge extra for a document which is required by regulations?


Excuse me, if I am being ignorant, but who are these 'engineers' ?
 
In the NECIEC world you would do a EICR before a CU change but in the real world that aint going to happen hence why I do a global IR test and ZE PFC then check the earthing 30 minutes tops so at least I have a good idea what I am going into or not the case in a 1950s house wired in MICC and most of the cables <2meg
 
I'm still struggling to grasp how an engineer is requested to change a CU without testing? Surely someone must have carried an EICR for the request to be made??
Then, I can't understand how engineers do not submit test certs as standard for a CU change? How can you charge extra for a document which is required by regulations?

WTF? what if the customer just decides it's time to get their consumer unit upgraded? This forum has went mad!
 
There are two ways of quoting for a requested CU change.

1.Spend time carrying out tests to establish if the CU change is going to go smoothly...in order to be sure a simple IR test is insufficient,continuity and ring continuity tests would need to be carried out as well.You are going to look a tool if you declare the install fit at the quoting visit IR test and then find during the change that a ring is broken and extra cost is involved after all.All this would be FOC if you then fail to get the job.
2. (my way).....The quote covers a CU change and any upgrades to earthing/bonding,as well as a full test prior to energising.It is made clear that testing may show up unseen problems which the client will be made aware of and may incur extra cost to rectify.

Both ways are equally valid IMO...take your choice.
No 2 has worked perfectly well for us ever since CU changes became fashionable and I expect it to continue to as well.
 
My point is that someone would replace a CU without prior inspection. It's been covered in great detail on here recently why some would or some wouldn't. For me, I would carry out testing prior and post CU replacement, but that's my opinion and I'm certainly not resulting to bad language or being aggressive to state it.
 
There is something that most on here are forgetting.
A Quote is a fixed price for doing a job - can not be increased or decreased unless you issue a refund.
An Estimate may change by a little or a lot!

if you quote £300 for a CU change then you must change that CU for £300 and any extra work you find to allow you to change that CU you must legally cover out of you a*** pocket.

if you provide a written quote for CU change then invoice for £600 due to remedial work to allow you to change CU the customer could legally only pay £300 and tell you to FO and no court in the land will back you!
 
With regards to testing a job 3hrs away I test it 2 mins before starting the Job. Prior to then I issue an estimate with conditions, then issue a quote for doing the work depending on what I find.

Estimates are normally provided over the phone for these with clear advice about bonding and faults.
 
Thanks to everyone for replies, first of all I have to agree with wirepuller on his quote that when running a business it is simply unrealistic to carry out testing before quoting a customer for a board change. So well done to you for your honesty. I do, however always carry out a visual check to see that the condition of the wiring is in suitable condition to re-terminate into a replacement consumer unit. There have been many occasions where I have politely declined to replace the consumer unit stating that an upgrade of the wiring would be required

Secondly I always provide certification post board change. On this occasion I had started the board change late on in the day and encountered this problem late on. I, of course, restored power to the property temporarily and then first thing in the morning revisited property where, thanks to some of the more helpful comments, I managed to quickly trace the fault to a junction box below the floor which had a damaged cable resulting in a N - E fault. This was quickly rectified and the RCD reinstated, installation tested with satisfactory results.

By the way I would like to state that I am in no way a Electrical Trainee! I have been in the trade for a long time and have completed the 2391 and have been very involved with electrical inspection, testing and certification since. I merely posted a problem I was having with a view to receiving some feedback with some ideas of where the fault most likely would be. I must be under the illusion that this was the purpose of the forum. It did seen though that as soon as some criticism was raised a lot of other forum members jumped on the bandwagon, slating me, presuming I was a Electrical Trainee/cowboy that had to clue or inclination on testing. It does seem that some of the members revel in jumping on these situations as soon as the opportunity arises. To those members I do apologise that I am less gifted than yourselves!!

I wish I did have the time to carry out a full test before quoting for consumer unit replacement but the trade is on its knees as it is and to be asked to carry out a board change these days instead of customers getting the work done as a homer is a rare occurrence in these parts
were still not getting it are we...

testing proves what you can`t see
 
I would agree that under most conditions that powering up before testing isnt right but on a domestic CU change where there are no circuits added/altered and everything was functional before then like Dr Pepper says the worst that can happen is a tripped RCD, as in this instance, the fault was rectified. This is getting boring now!
so...you clearly have no knowledge of the operating curves for different OPD`s either ...do you...
like BS3036`s for instance...
carry loads of fault they will....
 
I'm still struggling to grasp how an engineer is requested to change a CU without testing? Surely someone must have carried an EICR for the request to be made??
Then, I can't understand how engineers do not submit test certs as standard for a CU change? How can you charge extra for a document which is required by regulations?

Why would you ask an engineer to change a CU in the first place? You need an electrician for that, and they are most certainly not the same thing.

Does anyone else get p'd off by people who confuse the two?
 
No EICR is required, most of my CU changes come from the client just wanting to upgrade to an RCD after seeing a campaign in my local paper placed inline with a campaign I'm running along with the ESC about RCDs

Your running a campaign in the paper to drum up work for yourself, seems like a good plan but what exactly does this campaign entail?
Is it the standard 'the world will end if you don't have rcd's installed' style of thing?
 
There is something that most on here are forgetting.
A Quote is a fixed price for doing a job - can not be increased or decreased unless you issue a refund.
An Estimate may change by a little or a lot!

if you quote £300 for a CU change then you must change that CU for £300 and any extra work you find to allow you to change that CU you must legally cover out of you a*** pocket.

if you provide a written quote for CU change then invoice for £600 due to remedial work to allow you to change CU the customer could legally only pay £300 and tell you to FO and no court in the land will back you!

A quote can be a fixed price for changing a CU....but it can still be made clear that problems resulting from testing prior to energising the CU will be at extra cost.
I go back to my previous posts,a few basic tests on the pricing visit is undoubtably a good idea but cant eliminate the necessity for extra work when full testing is carried out during the actual CU change.Only a full EICR style test and inspection on the pricing visit can do that,and I'm not doing that for nothing.
 
I fully agree to the arguments of full testing, the only tests I do prior to changing a cu is global IR tests. Good results lets crack on! Not good results then talk to customer and ask them how they wish me to proceed. At least you know they have authorised it.
on day of change IR if not already done and continuity readings any issues back to customer.
you must have it good where you lot (ones who can charge extra and customer pays) are from as down here if I price a job up and even the customer changes plan they still refuse to pay not long if I throw up some faults!
 

Reply to Nightmare of a day. RCD tripiing under any load in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
349
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
588
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock