Discuss NO cpc lighting 18th edition in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
38
Went to fit new light fittings in a loft conversion today.
The existing ceramic half moon uplights were installed using 2 core flex buried in the plaster going I know not where!
I've come across 2 core systems in old peabody trust estates that where complient as long as double insulated fittings were installed, not extended and a warning label fixed to the fuse box.
Questions:
Are the old 2 wire lighting systems, providing insulation etc checks out, still legal retrospectevly under the 18th?
I know I cant extend a "cpc less" system. Am i going to have to tell my customer that this wiring is non-complient and needs to be replaced?
I know the answer but hoping for straws to clutch!
Cheers
Steve
 
The 2 core flex May Not go very far back into the wall and join to T&E.
Does the flex look like it came with the uplights?
No unfortunately, they didnt come with lights.
It's a 'designer' styled flat with the ceiling removed and the roof boarded out and immaculate mat white paintwork. I have no access to any possible JBs, switchlines etc without chopping away chunks of the ceiling. The least disruptive thing i could do would be go the SFCU route and use wireles switch relays (Lightwave RF or similar) . Any other ideas?
Cheers
 
You’ll possibly find a buried connector block in the plaster, wrapped with tape.
Check the other lights and switches for cpc’s.
Might be the case but its a gamble and my customer wont like it. The other option would be to use double insulated and sign of an exception but that's changed under the 18th hasnt it? No a great solution anyway when the next cowboy installs metal light fittings!
 
The ones you found might not have been unsafe with all the measures you mention, but it's not correct to state that they were compliant.
No, I meant the peabodyones are compliant as long as they remain in good order because they were allowed at the time of installation.
Theytremained complient as long as class 2 fittings are used.
I dontthink I can do that with this installation because it wasnt complient when installed.
 
It is for AC final circuits supplying luminaires. However is that retrospective applying to circuits installed to earlier BS7671 editions. There is no specific statement on the in the 18th edition. Practically that means if someone wants an extra light we now have to put in RCD as in sockets. This means most will baulk at the extra cost and get someone in who will do it without RCD. And in the case of the OP with no cpc an interesting conundrum.
 
I had a similar issue putting a bathroom fan in and NAPIT technical confirmed there has to be an R1R2 on any accessories you install. Ended up running a 2.5 single up the side of the house and into the loft.

My test if unsure is how confident I'd be explaining myself to a sarcastic lawyer in court.
 
I had a similar issue putting a bathroom fan in and NAPIT technical confirmed there has to be an R1R2 on any accessories you install. Ended up running a 2.5 single up the side of the house and into the loft.

My test if unsure is how confident I'd be explaining myself to a sarcastic lawyer in court.
A cpc not mechanically protected needs to be a minimum of 4mm^2.
 

Reply to NO cpc lighting 18th edition in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
740
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
664
Hello everyone, hope all are well. I'm changing a ceiling rose and have lost the diagram showing where everything was connected (to the old light)...
Replies
8
Views
941
Hi, Just interested in learning what others do when faced with an old lighting installation where there is no earth and you’re installing a metal...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock