Discuss No L-L end to end on ring main in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi everyone hopefully someone can shed some light.

I'm doing an inspection and test and upon testing my end to end for the live on a ring main I've found there is no end to end on the live. I've tested at sample socket and at the board. I got an r1 + r2 when interconnecting my lives and cpcs and a Zs. Just want to make I'm not missing something obvious. It's not my test kit as I've already tested two other ring mains

Thanks in advance
 
Did you originally test for continuity in a different place that you tested your figure of 8 test? If yes then the fault was where you 8’d, if no then you need to break it down as Sparkychick suggested.
 
Think about it, its a ring final so you will get an R1/R2 value and an internal loop impedance
 
I'm doing an inspection and test and upon testing my end to end for the live on a ring main I've found there is no end to end on the live. I've tested at sample socket and at the board. I got an r1 + r2 when interconnecting my lives and cpcs and a Zs. Just want to make I'm not missing something obvious. It's not my test kit as I've already tested two other ring mains
are you in training ?on site guide will give you that information or guide note 3.
 
Aye up @sparksburnout is back!
How many bans can one member get?
Just a joke - I know you’ve been a good boy and just lurked, biting your fist at certain times!
I've only been banned twice actually. nowt much changes though! I thought people doing I&T were supposed to be of a certain sort of experience level? Just saying.
 
QUOTE="Rpa07, post: 1486832, member: 66332"]Aye up @sparksburnout is back!
How many bans can one member get[/QUOTE]
th
he has more bans then football player .:D
 

Reply to No L-L end to end on ring main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
294
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
910
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock