Good morning... been called out to replace a DB on this domestic supply... no earth noticed and only bonding is 6mm from the incoming water supply...















Any advice as to how to document this would be greatly appreciated.. would like to get certification correct without any guess work...















Was a late call out to view the current setup so haven't done any Ze or pfc testing as yet...








Screenshot_20230307_103553_Gallery.jpg







Thanks in advance...












 

Attachments

  • Screenshot_20230307_103434_Gallery.jpg
    384 KB · Views: 44
It looks old and I have seen that before when it was using the water pipe as a means of earthing, something that has not been permitted for a few editions and many decades of the wiring regs! Historically that would often get a low enough Ze to allow OCPD-based disconnection on most fuses but obviously is no longer permitted for various reasons, the use of plastic water pipe being the most obvious one that would render ADS impossible.

If the DNO can't/won't provide a supply earth it would need to be made TT with a rod and suitable means of achieving ADS (realistically, RCDs all round).
 
There are loads of old places around me where the sole means of earthing is via a single bond to the incoming water pipe

Sometimes I have managed to get the DNO to make it a PME , and sometimes I get no joy with the DNO and have no choice but to TT it

One old massive house I went to change some electric heaters that had a Zs at a socket 250 some odd ohms , so I investigated further to find the entire house was relying on a 1.5mm green wrapped around the water pipe
 
It looks old

Old but not truly ancient. Note the white phase marker disc pinned to the meter board to the left of the service cable.
 

Reply to No sign of Earthing...? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
294
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
544
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
407

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock