Discuss Not getting correct voltage at outlets in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hello, new poster here, hopefully I’m doing it right. I have several outlets in my kitchen that aren’t working. They all have the same symptoms. I have the proper 125 volts From the hot wire to ground, but I’m only getting 109 volts from the hot wire to neutral. They are on the same circuit as my dishwasher and garbage disposal, both of those are working fine. The strange thing to me is it is all being fed from a double breaker at the panel. Thanks for any guidance you can offer.
 
There is probably a high-resistance connection in the neutral at the last outlet that works normally, or the first one that doesn't. The resistance is high enough that appliances do not work, but not completely broken, therefore the multimeter / voltage tester can still detect the presence of a voltage hot to neutral. The actual voltage you see on the multimeter does not signify anything in particular, only that the resistance in the circuit is in the same order as its own input resistance. If you connect a non-electronic appliance to any non-functional outlet while watching the meter, you would probably see that 109 volts collapse to near zero.
 
There is probably a high-resistance connection in the neutral at the last outlet that works normally, or the first one that doesn't. The resistance is high enough that appliances do not work, but not completely broken, therefore the multimeter / voltage tester can still detect the presence of a voltage hot to neutral. The actual voltage you see on the multimeter does not signify anything in particular, only that the resistance in the circuit is in the same order as its own input resistance. If you connect a non-electronic appliance to any non-functional outlet while watching the meter, you would probably see that 109 volts collapse to near zero.
Thanks for the response. I figured it was probably an issue with the neutral. The circuit seems to start at an outlet under the sink that the dishwasher and garbage disposal plugs into. Both those appliance work properly. It all four outlets that appear to be losing the neutral. I’m thinking the outlet that the appliances are plugged into might be the problem?

Is it common to run a double 250volt breaker to run a 125 volt garbage disposal and dishwasher?
 
This could be a multi-wire branch circuit, if it has two hot legs sharing a neutral, perhaps as far as the appliance outlet, continuing on to the remaining outlets with just one of the hots. Since the problem appears to be with a neutral connection, this is not strictly relevant. However it is worth noting that a disconnected neutral in the multi-wire section of the circuit can cause up to 240V to appear at a 120V outlet.

Your broken connection is likely to be at one end (we can't tell which end) of the cable connecting the outlet that works to the nearest one that doesn't.
 

Reply to Not getting correct voltage at outlets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
580
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
858
Hello, I live in Costa Rica, which adopted the US electrical code. On a regular basis, during thunderstorms, I have parks coming out of the...
Replies
0
Views
448
Wiring to new dishwasher causes garbage disposal to stop working. I just installed a GE dishwasher and came across a problem with the...
Replies
1
Views
711
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
927

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock