As above, Fluke has this where you null leads for loop testing.
Megger does not.
However the newer Meggers (e.g. 1700 series) have an option in the settings to adust lead resistance. I think the default's something like 0.07 Ohms for a standard lead set, but this may need to be altered for fused leads etc.)