As above, Fluke has this where you null leads for loop testing.

Megger does not.

However the newer Meggers (e.g. 1700 series) have an option in the settings to adust lead resistance. I think the default's something like 0.07 Ohms for a standard lead set, but this may need to be altered for fused leads etc.)
 
As above, Fluke has this where you null leads for loop testing.

Megger does not.

However the newer Meggers (e.g. 1700 series) have an option in the settings to adust lead resistance. I think the default's something like 0.07 Ohms for a standard lead set, but this may need to be altered for fused leads etc.)

Sorry this is not related to live loop testing but your post made me think about the 1700 series..

I hate the 1700s for the way they do not display negative values. The 1552 and. It's ilk were much better in that way and you could easily and confidently do simple maths to get end to end values etc without endless button pressing.. also those blo0die silicone leads... gggggrrrrrrrr!!
 

Reply to Nulling Test leads in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, just looking for a bit of advise. I am booked up to go on 2391-52 soon, and was looking at using my own tester, Megger1552. It is all...
Replies
5
Views
335
So, I was messing around yesterday with some old testers I have laying around to see if they still work I found my dads old Robin MFT and noticed...
Replies
8
Views
554
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi I've got a megger mft 1720 that I was hoping any one can shed any light on When performing continuity tests (even when nulling the leads)...
Replies
13
Views
2K
Morning everyone I’ve recently bought a fluke 1662 as my megger 1741 broke on a site last week. Does the fluke have the same capability as the...
Replies
4
Views
958

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock