Without looking does that mean the ocpd is oversized for a 6.0 cable?The last 500mm drops down inside a partition.
Discuss odd one seen today, three FCUs each for a 3KW immersion on one 6mm radial in the UK Electrical Forum area at ElectriciansForums.net
Without looking does that mean the ocpd is oversized for a 6.0 cable?The last 500mm drops down inside a partition.
If it’s the solution it’s the solution ......
Why do you say it’s price prohibitive
If the customer won’t pay to do it properly , just walk away
I know but there already there with the flexes run in so rather than have to patch the holes, just use them.If you put in a CU with 3 16 amp MCBs you don't need FCUs as well.
No but close. Like I said upthread someplace, It's all clipped direct bar 0.5m but that will be by the time I've finished.Without looking does that mean the ocpd is oversized for a 6.0 cable?
I wish, I'm asked to make it work and given a spend limit. Running three new circuits is above that.
Not ideal is not necessarily non-compliant.
How much difference between doing it properly and budging it to the budget?
I 'like' it too but aesthetics butter no parsnips.I like George's idea and fit flex outlets where the original 13 amps spurs are , or is there no budget for parts
I know but there already there with the flexes run in so rather than have to patch the holes, just use them.
OK, consider this, 3kW at 240v is 12.5 amps. Your voltage may be above this at 245v so 12.76 amps. If the immersions are rated at 3kW at 230 volts we would have 13.04 amps at 230v or 13.6 amps at 240v, 13.9 amps at 245v. Don't forget the voltage is allowed to rise to 253v.
Anyway the 13 amp fuses are going to run hot at these sort of continuous loads with subsequent damage to the FCUs.
Is that maths right? should the Amps drop as the Volts rise?
They are, now, on dedicated circuits.Oughtn’t we be putting known fixed loads over 2kW on dedicated circuits any way?
I’m with Murdoch; do it right or not at all.
How about din rail box with 3 x b16 mcb,s?They are, now, on dedicated circuits.