Discuss odd rcd trip times with a metrel? in the Electrical Tools and Products area at ElectriciansForums.net

dcwuk

-
Reaction score
0
Occasionally when carrying out rcd testing with a metrel 3100 I have had failures which upon investigation have been caused by me inadvertently leaving a piece of equipment connected to the cct the readings being x1=156 x5=>40 unplug or disconnect the piece of equipment and the readings return to normal. This as happened on various installations and the equipment that was found to be in cct always has a motor (fridge ect) Has anyone else experienced this problem?
 
Last edited:
Occasionally when carrying out rcd testing with a metrel 3100 I have had failures which upon investigation have been caused by me inadvertently leaving a piece of equipment connected to the cct the readings being x1=156 x5=>40 unplug or disconnect the piece of equipment and the readings return to normal. This as happened on various installations and the equipment that was found to be in cct always has a motor (fridge ect) Has anyone else experienced this problem?

Why are you concerned about these times?

Yes leaving an appliance plugged in can affect tripping times on an RCD, but those times you have posted are more than acceptable.

Though it is easier to plug the BS 1363 lead into a socket to test and RCD, I always try and do it at the CU just to save me going around and unplugging things
 
Thanks for the replies. this particular job is in an hotel where I am replacing mcb`s for rcbo`s and because I am testing the impedance of the ccts and the boards legends are inaccurate I am testing the RCD at the room rather than at the DB. The question is are the trip times an anomaly or is the appliance in fact preventing the RCD tripping within the times? I probably need to try another RCD tester on the Circuit and in the meantime have emailed Metrel for advice. I just wondered if anyone else had come across this problem?
 

Reply to odd rcd trip times with a metrel? in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
539
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
Replies
7
Views
2K
Testing an Ashley & Rock BS4293 RCD Type AC (CU dated 1989, property built c. 1990-91) this morning with a Metrel 3152 on RCD Auto; x1 and x5 were...
Replies
7
Views
3K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock