Tested an RCD spur earlier with some odd results

Tested at x 1/2 (both waveforms) and no trip
x 1 (0 degrees = 28.5 ms), (180 degrees = 18.4 ms)
x 5 (0 degrees = 8.2 ms), (180 degrees = 40 ms)

S0 getting bang on 40ms at x5 on 180 waveform; i know its in limit but was expecting it to be (at least) as low as the x5 0 degrees result.

The supply is TNCS, the circuit has low Zs, testing carried out at rcd spur itself, with load side disconnected. Tried it with two different sets of leads and same result, the testers been recently calibrated.

What would you do in this situation ?? I realise the x5 result is within limits (just). Really im perplexed, if this result is due to the nature of the waveform, or if the RCD is iffy.

And to add to the mix im reading that x5 rcd tests are , strictly speaking only required where your max Zs values cannot be met.. e.g. TT installations.
 
Last edited:
Tested an RCD spur earlier with some odd results

Tested at x 1/2 (both waveforms) and no trip
x 1 (0 degrees = 28.5 ms), (180 degrees = 18.4 ms)
x 5 (0 degrees = 8.2 ms), (180 degrees = 40 ms)

S0 getting bang on 40ms at x5 on 180 waveform; i know its in limit but was expecting it to be (at least) as low as the x5 0 degrees result.

The supply is TNCS, the circuit has low Zs, testing carried out at rcd spur itself, at load side with circuit disconnected. Tried it with two different sets of leads and same result, the testers been recently calibrated.

What would you do in this situation ?? I realise the x5 result is within limits (just). Really im perplexed, if this result is due to the nature of the waveform, or if the RCD is iffy.

And to add to the mix im reading that x5 rcd tests are , strictly speaking only required where your max Zs values cannot be met.. e.g. TT installations.
How many times did you carry out the tests? could be just a glitch
 
5x rcd tests on 30mA rcd’s are for the circuits circuits requiring and covered by said rcd and require additional protection so must trip within 40mS @ 150mA regardless of what type of earthing arrangement is in place.
 
5x rcd tests on 30mA rcd’s are for the circuits circuits requiring and covered by said rcd and require additional protection so must trip within 40mS @ 150mA regardless of what type of earthing arrangement is in place.

Yeh additional protection against direct contact , x1 tripping times below 200ms would account for that where the circuit has a low enough ZS would it not ? I know the regs state x5 have to be within 40ms for TN systems too, but thats' backup to protect against a low high Zs scenario aint it
 
Last edited:
Yeh additional protection against direct contact , x1 tripping times below 200ms would account for that where the circuit has a low enough ZS would it not ? I know the regs state x5 have to be within 40ms for TN systems too, but thats' backup to protect against a low high Zs scenario aint it
It’s got Nothing to do with back up of anything or a high zs.
A 100ma rcd would be suitable for a high zs on a TT for fault protection for circuits where additional protection is not required however it’s not a requirement to test a 100mA rcd at 5 x the rated current as it does not afford additional protection.
Only a 30mA rcd will offer additional protection and 40ms is the time given before an electric shock could become fatal.
Hence at 150mA it must disconnect in 40ms or less
Bs en 61008 rcds for 30mA
1x test for fault protection, must disconnect in 300ms or less
5x test for additional protection, must disconnect in 40ms or less
 
Last edited:
It passes....but ...only last Saturday I had to return to a job I had installed sockets on TT using a safetysure FCU...it had only lasted 2 years. Not fitting that again, they are a good price for a reason ...it will be a power breaker now.:rolleyes:
 
1x test for fault protection, must disconnect in 300ms or less
5x test for additional protection, must disconnect in 40ms or less

Aw right, will have to get my head round that, nice one. Where I was going with ZS scenario sounded right in my mind but hey ho potatas/potatoes , u learn something new every day :rolleyes:
 
What has Zs
Aw right, will have to get my head round that, nice one. Where I was going with ZS scenario sounded right in my mind but hey ho potatas/potatoes , u learn something new every day :rolleyes:

Will an MCB operate at 30ma!

The RCD is being used for additional shock protection due to failure of basic protection/carelessness of user etc. it should operate before the end user receives a fatal shock.

The MCB offers protection to the cable.
 
What has Zs


Will an MCB operate at 30ma!

The RCD is being used for additional shock protection due to failure of basic protection/carelessness of user etc. it should operate before the end user receives a fatal shock.

The MCB offers protection to the cable.

Yes when you put it like that it all makes sense now. Feel rather sheepish now tbh to have made such a daft assumption. I mean the ZS itself wont affect the trip time will it :oops:. Will be reading up again on this subject and nail it.
 

Reply to Odd test results on RCD Spur in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning everyone, this is my first post - although i had an account years before that seems to have been lost. Can any of you shed some light...
Replies
24
Views
5K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
I tested a customers BS4293 MEM 100A, 30mA RCD, which is about 25 years old, after it tripped overnight. The trip time at x 1 was 207.2, 78 and...
Replies
28
Views
5K
I hear many views of people who believe that DPF's and CDPF's fitted to their vehicles are a problem and many people resort to removing them, or...
Replies
0
Views
8K
To keep your trainee brains in tip top condition during lockdown, here's a few quiz questions.... 1) A fault report is 'Circuit breaker keeps...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock