Discuss Ohms Law and low voltage in the UK Electrical Forum area at ElectriciansForums.net

If you manage to prove Ohm’s law wrong, can I be your agent? I’ll only want 15% of the fortune you’ll make.

(Discounting supper cooled conductors).
 
How come Ohms law doesn't apply when talking about low voltage downlights. i.e 50w divided by 12V = 4.16A so thats obviously wrong. I think Im getting a bit confused.

A 50W 12V lamp will be drawing 4.17A through the ELV cables and then on the other side of the transformer (ignoring transformer losses), 230V using 50W will be drawing 0.22A on the LV side.
Try a clamp meter on the ELV cable to a downlight and measure the current.
 
think the OP is confused by not converting the current to the primary 230V and thus thinking 1 50watt lamp will draw 4+ amps from the 230V supply.
 
Have been asked several times by customers How much am I saving by having 12v 50W lamps instead of 50W mains - if anything it will be costing more due to the transformer losses, but 50W is 50W.
 
It’s raised a question for me. Why the hell are they so popular?

It’s been bugging me for a while, (since I joined this board). They don’t make economic sense.

Is it just kudos on the part on the customer giving bragging rights, (we’ve got these new low voltage lamps in our kitchen, etc). Or marketing gobbledygook by the manufacturers.

As D80 says 50W is 50W + losses. So for 50W with transformer losses of say 1.5% (generous) you use 50.75W.

I thought we were supposed to be GREEN.

If I’m wrong please correct me.
 
It’s raised a question for me. Why the hell are they so popular?

It’s been bugging me for a while, (since I joined this board). They don’t make economic sense.

Is it just kudos on the part on the customer giving bragging rights, (we’ve got these new low voltage lamps in our kitchen, etc). Or marketing gobbledygook by the manufacturers.

As D80 says 50W is 50W + losses. So for 50W with transformer losses of say 1.5% (generous) you use 50.75W.

I thought we were supposed to be GREEN.

If I’m wrong please correct me.
Probably should not get into this one!:38:
You are not wrong, in my opinion.
But they are so safe because they are separated 12V (with 230V just next door, lots more connections and a transformer to go wrong).
The lamps have thicker filaments so they won't break so easily (depends only on lamp quality)
The light quality from 12V is so much better (barely noticeable)
12V can go in a bathroom safely (so can 230V, OK maybe more flexibility with separated 12V)
So for an additional cost, with additional components, additional energy losses, more space required in ceiling for transformer they are so much better:confused:.
Someone else will probably cut me down, oh well!:74:
 
My mate has just built himself an extension on his house to make a kitchen / diner.

He's wanting to put 20+ of these damn' downlighters in it !!! :hanged:
 
My mate has just built himself an extension on his house to make a kitchen / diner.

He's wanting to put 20+ of these damn' downlighters in it !!! :hanged:

LED and he'll be alright.
 

Reply to Ohms Law and low voltage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Currently I have 4 small low voltage transformers connected to 4 circuits of low voltage yard lights. They are under my deck, and I turn then on...
Replies
5
Views
3K
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi guys, I am new to the forum so be nice! I used to install solar PV systems back when the tariffs were still good, and I've never had to go...
Replies
5
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock