polo1

-
Arms
Reaction score
633
Guys/gals, a cast iron three phase head with a PILC incomer, with what appears to be a light brown oil coming from the head down the incomer (soz, no picture as flash would not work). The head is in a domestic property delivering single phase.
Any ideas what the "oil" is and need I be concerned/notify DNO?
 
if its a cast iron head then it definitely needs replacing, and could date back to the 20,s the oil / bitumin thats oozing could be a sign there is a problem , if im not mistaken these fuses were wire, can you get a pic
 
Last edited by a moderator:
Surely if it looks like oil it's not the bitumen but the cable compound. The paper in PILC cables is impregnated with an oily insulant to prevent it absorbing moisture, and one of the purposes of the bitumen is to keep it in the cable. If you look on the floor of an old switchroom with lots of PI cables you will sometimes see odd splodges of compound. Leakage may or may not be important, now I think about it I don't generally take much notice of a light ooze but a puddle should be reported.
 
Thanks guys. I did wonder about bitumen but where I've come across this before it's been black and more of a runny tar consistency. This stuff looks more like dirty 3 in 1. I'm due back Fri or Mon and have now sorted the camera on my phone. So a pic will be taken.
Replacement of CI heads - that's a laugh. We have thousands of these with no programme for routine replacement. The DNO simply will not invest in a replacement programme; hard enough to get them to replace even where there's a fused neutral. Again, thanks for the feedback.
 
No need for the poorly disguised expletives in the public forum ... Im sure you could have made the same point without resorting to this level there are many less offensive ways of saying the same thing and getting your point across just as strong.
 

Reply to "Oil" from cast iron head in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock