Existing circuit of 6mm t/e to 6.6kw 4 ring hob. Can x 2 single ovens of 2.1 kw each be added to this 6mm radial.
Total of 10.8 kw and 45A but 21A with diversity. Would this be considered ok
Theory sounds ok and unable to get 2nd cable in but not feeling happy with it.
 
it will be fine on a 32A MCB ( or 40A if ref. method C). only drawback will be the fact that you can't isolate separately, unless you add 1 or 2 more isolators.
 
Thanks for thst.
Cable is clipped to joist underfloor.
5m from csu to hob isolater. It is then 5m to oven point where I will put 2nd isolator to feed 2 13a fused connections for ovens.
Any tips on extending the 6mm from hob as loop in/out at hob isolator sounds difficult to fit.
 
6.0mm wagos in small adaptable box under floor or low level concealed in base units if required to be accessible.
 
Hi - also the cooker isolators will often take 3 x 6mm, well the BG ones do :) .

IMG_1130.jpg
 
come off the connection unit in 2.5mm to unswitched socket or FCU, depending on whether ovens have a fitted pug.
 

Reply to One circuit for hob and 2 ovens in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all Some advice on this would be great. Due to wire a kitchen from scratch and in a pickle over the designing of the oven and hob circuits due...
Replies
6
Views
2K
Hi, we are replacing our old hob and cooker and I need a bit of help, to make sure all is safe. This is the oven and hob specs: AEG IKB64401FB...
Replies
0
Views
2K
I intend to install a 32A 4.8kW oven and a 13A 3.7kW induction hob on an existing 40A breaker with 6mm cable. Will this be OK?
Replies
4
Views
2K
Howdy experts, I normally run 6mm T+E for cooker circuits, housing authority spec. I'm changing my gas inbuilt double oven and hob for...
Replies
9
Views
3K
Howdy All, just after a 2nd opinion as i'm doubting myself. I went to a property to look at replacing the ccu, I noticed what I thought was a...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock