    Hi - My first post to this forum.

    I am having a disagreement with another electrician on the type of the supply characteristics for a domestic installation, i.e. whether it is TN-S or TN-C-S. I have uploaded a photo of the cutout/supply head. To resolve the disagreement I suggested we ask for a 3rd, 4th, 5th .... opinion from the forum.

    The building is in a suburban area and is over 100 years old , not that I am suggesting that the supply head is that old. There are no PME labels/markings. The measured Ze is 0.11 ohms.

    Thanks for your views in advance.

    jlrb

    Supply Type.jpg
     
  2. Lee42
    Offline

    Lee42 Lee

    Location:
    England
    I would say TN-S
     
    • Agree Agree x 1
    • Funny Funny x 1
  3. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    only DNO could tell you for sure . rare to see supply in split concentric.
     
    • Dislike Dislike x 1
  4. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    Did you test L-N fault loop?
     
    • Like Like x 1
  5. Lee42
    Offline

    Lee42 Lee

    Location:
    England
    Did you have to remove the seals to gain access?
     
  6. jlrb
    Offline

    jlrb EF Member

    Location:
    London
    Yes that is what I though - however when I called UKPN they said that they do not have information on supply type. Go figure! So no help there.
     
  7. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    measure both pefc and pscc. if they are the same, i'd opt for TNC-S.
     
    • Agree Agree x 1
  8. jlrb
    Offline

    jlrb EF Member

    Location:
    London
    No, the seal was already broken.
     
  9. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    :eek::eek::eek::eek::eek:
     
  10. jlrb
    Offline

    jlrb EF Member

    Location:
    London
    Thanks - that was my thought on next step too if there isn't a barrage of consensus from the forum. Even then it will still be an inferred result which I was hoping to avoid.
     
  11. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    you could always dig up the supply cable and see where the earth is. :(
     
    • Funny Funny x 1
  12. jlrb
    Offline

    jlrb EF Member

    Location:
    London
    Ha ha - I bet the DNO would love that!
     
  13. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    TN-S
     
    • Agree Agree x 1
  14. jlrb
    Offline

    jlrb EF Member

    Location:
    London
    As Murdoch and telectrix suggested:

    Measured PEFC = 2.10 kA (0.11 ohms)
    Measured PSSC = 1.30 kA (0.18 ohms)

    This indicates to me that it is TN-S rather than TN-C-S, but I was expecting the relative values to be the other way around - but on reflection I am not sure why I should expect that.
     
  15. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    My "guess" would have been TN-S..................
     