It's been a while since doing any form of installation so I thought I may ask here for clarification especially with new regs......

Detached shed/building approx. 50m from house CU. Need to run 13A sockets and lights in it. TN-CS/TNS supply

Is it best to...

A) Take from MCB, then SWA down to RCD protected garage board with localised earth rod.
B) Take from RCD protected way to garage unit with/without RCD
C) As B but with earth rod also
D) Answer not above

Any help appreciated. I think I'll stick to commercial lighting... :)
 
A) is allowable
B) is allowable if there are no extraneous conductive parts in the remote building or if those parts are bonded back to the MET.
C) is allowable but it would be a nuisance to reset an RCD in the house (that has taken out other circuits)
D) this is possibly your best choice if there are no extraneous conductive parts in the building and so can do A without an earth rod.
 
It's an ex chicken shed; now storage/garden type shed. But it does have metal in the fabric of the frame; it's not just a timber garden type unit.
 
It's an ex chicken shed; now storage/garden type shed. But it does have metal in the fabric of the frame; it's not just a timber garden type unit.
Is you supply TNC-S or TNS. Metal work, generally has to be embedded in the ground to be extraneous, but test would confirm either way.
 
In my understanding of the definition, the metal is bolted/fixed into the ground (concrete base) therefore extraneous.

So it looks like I'll need to use a local rod and ensure the metal frame is bonded.

Any further advances???
 
Extraneous.

So, SWA from MCB, with NO connection to MET at CU, then RCD garage board with rod at shed???

Will that provide the RCD required for regs between CU and shed, or would that only RCD the shed itself?
Re my post #5, qualify what supply you have?
 
Last edited:
Did you have a test result for the suspected extraneous metal work? You'll have to decided whether to export your TNC-S supply or not to your shed. Any extraneous metal work may have an impact on your decision.
 
If the metal work is indeed extraneous and you've carried out a test to confirm this then you could extend the equipotential zone to the out building and bond the metal work. You could to this by running a separate bonding conductor, sizing it correctly by bearing in mind the earthing arrangement is tncs and it would also have to comply to the minimum csa for direct burial due to corrosion etc. The other/easier option Imo would be to use a 3core SWA and size it appropriately so the CPC could act as as a combined bonding/circuit protective conductor.
 
Last edited:
Did you have a test result for the suspected extraneous metal work? You'll have to decided whether to export your TNC-S supply or not to your shed. Any extraneous metal work may have an impact on your decision.

You're not exporting anything, just extending the equipotential zone.
 
Extraneous.

So, SWA from MCB, with NO connection to MET at CU, then RCD garage board with rod at shed???

Will that provide the RCD required for regs between CU and shed, or would that only RCD the shed itself?

No, to create a Seperate TT earth the armour must be connected to the earthing system of the installation it is fed from and must meet the requirements of a cpc (or have a core used as a cpc connected) this then would be isolated at the load end with a plastic gland/heat shrink etc and a separate earthing system create by use of multiple properly installed earth rods.
 
You say to-may-toes and I say to-mah-toes. Ohh, how tiresome.



You said 'exporting the TN-C-S supply'

I said 'extending the equipotential zone'

I wasn't being flippant like your reply, just simply pointing out the error.
 
Last edited:

Reply to Outdoor Building Power in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
2K
The garage is 17 mtrs x 15 mtrs in the UKh The house has a 100 amp supply to the house consumer unit. The garage consumer unit is fed from a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock