Discuss Outdoor LED flood dimmer? in the Lighting Forum area at ElectriciansForums.net

LeeH

-
Esteemed
Arms
Reaction score
1,173
Im after dimming 4 of the floods below, the seem a nice fitting for the money.

Suitable IP rating would be preferable but I'm propaged to use an enclosure if necessary.

http://www.NoLinkingToThis/p/luceco-guardian-slim-led-led-floodlight-10w-black/4483h


Cheers!
 
How do you know they are dimmable, most won't be.
 
You will probably need to buy new units that do colour changing AND dimming...

My limited experience with those are that the warm white is more of a yellow. Excuse the link to the cool white fittings.

I guess I'll swap them out with dimmable warm white floods. If possible..
 
They are not dimmable.
LED's that are dimmable usually say they see.
You also need to use a leading edge dimmer switch, as standard trailing edge dimmers need a minimum of 60w to work. And given most LED's are a lot less than that, they simply won't function.
 

Reply to Outdoor LED flood dimmer? in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Grateful for a kick in the right direction on the following: a telecomms engineer stated out that an outdoor metal cabinet (earthed & bonded) was...
Replies
22
Views
2K
It seems manufactures shy away from stating their IP rated CU’s are suitable for use outdoors - for example the BG IP65 one below which is metal...
Replies
6
Views
1K
Hi I have three rooms. Two rooms have two lighting points, each with 3 GU10's coming out and 1 room and one point with 3 GU10's. So I have 5 of...
Replies
22
Views
11K
D
Can anybody shine some light on LED dimming. I realise that led dimmers have a different rating for dimming LED bulbs ....( eg : 10w -100w) as a...
Replies
5
Views
944
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock