Discuss Outdoor lighting heating in the UK Electrical Forum area at ElectriciansForums.net

jsg_85

DIY
Reaction score
0
Hi guys

Just wanted some advice.

We wanted to get some lighting, sockets and a infrared heater to our garden gazebo. We have an outside socket currently right next to the gazebo. Could you guys give me some advise on a bit of a wiring diagram on the following, we wanted to have 2 double sockets, 2 led batten lights connected to a double switch and 1 3000w infrared heater (3000W Helios Infrared Bar Heater - https://www.suryaheating.co.uk/3000w-infrared-bar-heater-4230.html), also 1 security light on the outside of the gazebo looking out on to the garden controlled by a switch so we can keep the light on if we wanted to.

The plan is to come off of the outdoor socket currently in place, which is on a ring circuit with a 50a MCB connected to it.

Would it be a case of spur off one of the outdoor sockets to a 6a fuse spur to a double lighting switch to the lights? Then spur off the other outdoor socket to a 13a fuse spur to the heater?

Thanks in advance.

Jay.
 
Are you sure the ring circuit is protected by a 50A MCB?

Also, is there RCD protection?
 
Is your outdoor socket using standard three pin plug like the ones in your kitchen or are we talking about industrial type high power plugs?
MKK9733BLU.JPG

If it is a standard domestic one, then
for start, get a competent person to deal with the 50Amp issue, as its unlikely that the plasterer or a gardener who connected ring to outdoor socket to 50Amp breaker have known what he was doing and as such may have made other errors.
What it comes to with gazeebos its a question weather it is permanently fastened.
You will need suitable one of those on a picture above with builtin switch and deal with connecting the rest internally(within gazeebo). When it comes to 3KW items especialy if used frequently it is generaly good to look for a way to avoid using plugs with them and if so you need to make sure they are really clean and consider going industrial again... In mine opinion 3KV rating is too much for domestic socket and standard should lower it
 
Last edited:

Reply to Outdoor lighting heating in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
695
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
316
We have an outdoor socket that is hard wired into the ground floor power circuit and protected with an rcd in the consumer unit. I now plan to add...
Replies
17
Views
3K
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K
Hi, I have recently moved house and what to replace the garden shed. The shed has some electrics; a double socket with a fused light switch and a...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock