    Hi

    I'm just getting myself verified with Elecsa and I'm wiring my 1st job..Just come across a little sticking point!!

    Do I wire an outdoor security light off my lighting circuit or do I take it from a FCU spurred off the power circuit?

    The only reason I ask is that I always see security lights on spurs, could this be because they were added later?

    Cheers
     
  2. i=p/u
    Offline

    i=p/u Electrician's Arms

    just to prtect the light going outside which is more like to cause a fault... which is probably manufacture instructions
     
  3. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    you can do it either way to comply with regs. however, i always ( if possible) feed from a 2 pole FCU. then if there's a fault on the outside ( maybe by water ingress) it can easily be isolated by the client, thus allowing RCD/MCB to be reset.
     
  4. i=p/u
    Offline

    i=p/u Electrician's Arms

    thats what i ment to say, exact words
     
  5. HandySparks
    Offline

    HandySparks Forum Mentor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    If it's a higher power light, such as a 500W flood taking just over 2A, then you might put it on the power circuit rather than overloading the lighting circuit. You need to check what the existing loading on the circuit is and choose accordingly.
     
  6. dtec dave
    Offline

    dtec dave Regular EF Member

    Location:
    Leeds
    cheers...I have 3 security lights and 2 outdoor lights to fit, so think I am going to run them on thier own separate lighting circuit..good idea??
     
  7. cook1e
    Offline

    cook1e Regular EF Member

    If you can do it that would be a better way, think about how you can run the cables, which certificate you need to issue etc.
    Is the mains up to standard ? have you got enough money in the job etc

    Martin
     
Loading...
Similar Threads - Outdoor security light Forum Date
Electric shock from outdoor security cameras Electrical Forum Nov 25, 2018
Outdoor Cabin Feed Help Electrical Forum Tuesday at 5:31 PM
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job