Hi guys
Wanting to put an 8 watt led light fitting outside ,
Only place I can get a supply from is kitchen ring main got a radial approx 4th long.
now issue is the radial is already feeding combination boiler and a single socket for washing machine. If I put additional spur in for outside light am I getting to close for maximum load as like I said already got 13 amp for washing machine and 3 amp for boiler so with outside light with 3 amp fuse in spur then load going to be 19ampeven those new lights won't be pulling 3 amp tia
 
Home improvements, eh? So, is this a job you've taken on without an electrician? It is so basic.
 
Sorry 4mtrs long radial off of a rfc supply to a kitchen with 32amp mcb,
The radial currently supplies single one gang socket outlet to washing and fused spur to combine boiler,
Assuming the radial will carry 20amp safely?
 
washing machine will be no more than 10A when heating. just add a FCU with 3Aor 5A fuse for your outside kight.
 
washing machine will be no more than 10A when heating. just add a FCU with 3Aor 5A fuse for your outside kight.

Was so much better when washing machine had a hot n cold fill..
With the option of economy wash to bypass the heating stage of the wash..
Apparently, it’s more economical to heat cold water than to use stored hot water
 
Hi barnaby I'm unsure but I will test the circuit and see how I get on with results, assuming ill need to do a zs and ir test and compare again on site guide
Thanks guys for your replies was more just wanting confirmation that would be okay loading it up a bit more, provided I'm under 20amps
 
Couldn't see why you were talking about rfc and radial when only one circuit involved. It's all on one spur from the ring, I take it.
 
Hi no its a 2.5 radial of a rfc either out of a socket outlet or joint box but I can't get to find it . so I've got a radial into a single socket outlet with washing machine into it then into a spur for boiler
 
As above, it sounds like it doesn't comply as it is, even before you start adding more things to it.
 
Hi no its a 2.5 radial of a rfc either out of a socket outlet or joint box but I can't get to find it . so I've got a radial into a single socket outlet with washing machine into it then into a spur for boiler
no such animal Gary its a spur off an RFC which in turn feeds another spur, A radial will be fed from its own OCPD
Yes I've looked at appendix 15 and as uve said doesn't comply so won't be doing that then thanks for all the advice guys appreciated! !!
uve??
 
Hi guys
Wanting to put an 8 watt led light fitting outside ,
Only place I can get a supply from is kitchen ring main got a radial approx 4th long.
now issue is the radial is already feeding combination boiler and a single socket for washing machine. If I put additional spur in for outside light am I getting to close for maximum load as like I said already got 13 amp for washing machine and 3 amp for boiler so with outside light with 3 amp fuse in spur then load going to be 19ampeven those new lights won't be pulling 3 amp tia
Just say no
 

Reply to Outside light off an already used spur in 2.5t&e in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
Hi all, wonder if someone can help me. I've bought a bathroom extractor and I do have the wiring there already (previous extractor was there) but...
Replies
6
Views
2K
What is everyone's opinion on taking a combi boiler supply off the lighting circuit? I doubt the boiler would pull more than 300 watts and with...
Replies
22
Views
4K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hello I’m going to install a hard wired 230v security camera, incorporating floodlights, outside and above garage door onto brick. An exposed...
Replies
1
Views
976

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock