Discuss Outside socket on a spur in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

S

Stormflex

Morning all,

I have a customer who would like an outside socket fitted. There is a double socket inside their patio door.

Can I run this as a straight spur of the current socket or do I need to run it to a FCU first?

Thanks

Rich
 
The socket at the patio is it part of a ring final circuit or is that indeed a spur itself, if it's a spur of a ring final then no.

Is it part of a radial then yes you can spur off it.

How will you provide RCD protection for the socket if it does not already have it ?
 
Good point. I have assumed it is on the ring. The ring is protected by an RCD.

malcolmsanford - are you saying that if the socket is in a ring I can't spur off of it?
 
Last edited by a moderator:
if the existin g socket is on the ring, then you can spur off 1 socket without a FCU. if it's on a radial 16A cct. you can just add your otside socket. only if the existing socket is itself spurred off a ring do you need to fit a FCU.
 
HI Guys As you know i come from an It background and had thought that in the distant past they did allow a spur of a spur indeed the house i am in at the moment has one as did my previous place(until i had it fixed).

When did this practice stop and is it still acceptable as a old installation .

The one in my present house is a upstairs ring main with a non fused spur to a dbl socket which in turn has had three further doubles added after that one approx 10ft further on from the spur all looks tickety boo to my "non spark eye".(checked as best i can with my marindale and volt meter)
I use these sockets for low wattage equipment.
Should i be concerned and get it fixed or just leave alone as an old instal?
cheers 72-van
 
ideally you should fit a 13A FCU before the first spurred socket. this will limit the current drawn by your spur to within the capacity of the cable.
 
Hi Telectrix Thanks for that advice but were i to do that surely i would then be altering an old install and making it "illegal" my plan was to disconnect the extra double sockets which are connected after the original spaur part before selling the place thereby "keeping it right " to my non spark eyes.In the mean time the sockets are in use for devices that probably draw 5amps max between them & i am the only one living there.
Or should i bite the bullet and disconnect the spurred spur thing now and use an extension lead tp power this kit whats best ?

72-van

cheers 72-van
 
IMO I would fit it via a FCU for a couple of reasons. As said earlier with a switched FCU you can isolate the socket completely when not in use. Also if you ever want to work on it, you can isolate it via the switched FCU without turning off the whole circuit.

Saying that as long as it's just the one un-fused spur point off an existing ring final circuit or a radial there is no need for a FCU.

I was though in my OP more concerend about the RCD protection for this socket.
 
Hi Telectrix Thanks for that advice but were i to do that surely i would then be altering an old install and making it "illegal" my plan was to disconnect the extra double sockets which are connected after the original spaur part before selling the place thereby "keeping it right " to my non spark eyes.In the mean time the sockets are in use for devices that probably draw 5amps max between them & i am the only one living there.
Or should i bite the bullet and disconnect the spurred spur thing now and use an extension lead tp power this kit whats best ?
There is nothing illegal with altering or adding to old or existing installations.
I obviously don't know how old the existing installation is, but having more than one double socket on an unfused spur from a ring final circuit has not been compliant with the Regulations for about 30 years.
Installing an FCU between the ring and the first spurred socket would make the circuit more compliant, and as long as the work is not within a kitchen, would not require notification under Part P.
 

Reply to Outside socket on a spur in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
709
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
710
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
419
Hi all, My mother wants a double socket adding next to a desk, behind the desk there is a 10mm (i dont know the MCB in the Consumer Unit) which...
Replies
4
Views
1K
We have an outdoor socket that is hard wired into the ground floor power circuit and protected with an rcd in the consumer unit. I now plan to add...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock