Discuss overcurrent protection in the UK Electrical Forum area at ElectriciansForums.net

P

paddyscouse

hi can any one give me there view on what would be recorded in; the overcurrent protective device for the modified circuit on a domestic minor works cert ,for additional lights fed from a fused spur 3a witch is fed from the ring circuit ? would it be the 1362 fuse in the f sp or the 32 mcb at the c u..........
 
Re: ocercurrent protection

If it is a new lighting circuit fed from the fused spur then it is a new circuit with the 3A fuse as it's OCPD.
If you added the fused spur to the ring circuit then that is a modification to the existing circuit.
 
Re: ocercurrent protection

yes its a fuse spur added to r c that feeds the lights
thaks for that ill record it as the 1362 fuse ..........should i record the 80% zs values or normal value
 
It is a minor works job Dave as it doesn't involve the provision of a new circuit. It's an alteration to an existing circuit. And yes Paddy, it's the fuse which offers the overcurrent protection to the new part of the circuit, so that is what goes in the box.

As for the 80% value Paddy, what do you think you should record and why?
 
Last edited:
It is a minor works job Dave as it doesn't involve the provision of a new circuit. It's an alteration to an existing circuit. And yes Paddy, it's the fuse which offers the overcurrent protection to the new part of the circuit, so that is what goes in the box.

As for the 80% value Paddy, what do you think you should record and why?

i think it should be the normal values as said in the bs7671 requirements for elec instal as this is what the cert asks for as oposed to the osg values..... am not sure to be honest
 
i think its the values in the 7671 as this is what the cert asks for as oposed to the 80% in the osg

reasons for the 80% apart from the obvious the "lower the zs safer" im not sure.... what is correct
 
i think it should be the normal values as said in the bs7671 requirements for elec instal as this is what the cert asks for as oposed to the osg values..... am not sure to be honest

Those values are for when that cable is operating at 20°C. Under fault conditions that temperature is going to rise considerably increasing the resistance of the cable. The maximum permitted Zs values need to be corrected to take account of this rise in resistance.

I'll ask you that question again :D
 

Reply to overcurrent protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
777
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
841
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
866
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
503

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock