Discuss Overheating EV install in the UK Electrical Forum area at ElectriciansForums.net

littlespark

-
Esteemed
Arms
Supporter
Patron
Reaction score
17,121
Had a call from a parent of one of my daughters friends…

” Do you do electric car charge points”

“Well, no. Not installation, but I can diagnose faults…. Tell you what’s needed. “

“I’ve already phoned the supplier. Not interested. 3 weeks out of the warranty period. “


So here’s the charge point.

C96EEC55-A45D-4872-980F-5350C1596091.jpeg


And here is where I think the problem lies.

41BEFD73-46AC-46B7-AF76-049D22B950EA.jpeg


Ok. Severe overheating on supply neutral cable.

Easy enough to fit a new box, rerterminate the ends… but I’ve got a couple questions of the EV experts.

1. Heat caused by loose connection or over current? What load should this charge point be taking? Is it going to happen again if I replace this box and remake the joints.

2. What is the small core twisted cable with the red tip device be for?
 
I would say, based on the apparent lack of thermal damage on the line conductors (apart from where they've been toasted by the neutrals) it's down to a bad joint at the chock block they used on the neutral.

Edit:- I'd have a look at other points on the cable... if there's no signs of thermal damage anywhere else it's down to the termination not an overcurrent situation.
 
As it was -8 where i was, i wasn't going into too much examination of the entire installation.... but now ive got the feeling back in my fingers...

You can see the supply cable on the bottom left isn't an SWA. It's 3 core Tuf-Sheath or whatever... Ill check the route back into the house when i replace the box.

Earth rod somewhere under the snow. The earth wire goes down the flexi conduit on the right. Not connected to supply earth.

Short piece of flexi between top of box and charge point. Will have to replace the tails unless there's some spare in the charge point itself.

The box lid hardly fitted back on, as it was starting to melt too.
 
Definitely faulty connection, as the line is OK despite carrying the same current. Plus, if a terminal had been sound and of low resistance but the cable was overloaded, it would have overheated more where it is bunched and less at the terminal because that provides a heatsink.
 
No comments on the device with the red tip yet.
Looks like a small panel mount thermal current trip, like a MCB, but without the instant trip part.
No idea what it's got to do with a charge point though.
 
I’ve been having a Google looking for details of this charge point, and on a dedicated EV forum, someone mentioned a “push button in the junction box to switch between 16A and 32A”

So that might be what the red button does, and if so, I’m going to have to replace it.

Still looking for a decent installation manual showing connections, and possibly a set up procedure.
 
I’ve been having a Google looking for details of this charge point, and on a dedicated EV forum, someone mentioned a “push button in the junction box to switch between 16A and 32A”

So that might be what the red button does, and if so, I’m going to have to replace it.

Still looking for a decent installation manual showing connections, and possibly a set up procedure.

It doesn't look like it's IP rated, so was it actually mounted in the junction box in such a way so as to be accessible, and operable by the user?

If not, I would establish whether it's a simple push to make switch... if it is and it was not installed in a way to allow the user to operate it, I wouldn't worry about it.
 
90% certain that's a push button. What's it do? You've got to try pressing it - it's the law when you find a button!
as Sir Terry Pratchett put it:

“Some humans would do anything to see if it was possible to do it. If you put a large switch in some cave somewhere, with a sign on it saying 'End-of-the-World Switch. PLEASE DO NOT TOUCH', the paint wouldn't even have time to dry.”​

 
Been back at this job this morning and replaced the box, cut back all the melted cable and reterminated.

Going through the testing afterward and the earth loop was 125 ohms.
This is not from PME from house, but a rod. Found the top of rod just below charger, less than a metre away. No sign of corrosion.
Seems high to me, but as I’m not an EV installer, and don’t come across this on a daily basis, I thought I’d better ask you lot.

Left turned off just now. Customer is still away for new year, and got the electric car away so I couldn’t test it plugged in.
 
If they put in a 1.2m / 4' rod then 125 ohms is not very surprising, it would be what to expect from around 175 ohm.m soil resistivity which is about mid-range for most soil types. However, it would seem a touch high for a winter in Scotland with ground pretty damp sort of situation.

It does meet the 200 ohms for the regs and of course is well below the theoretical 1.6k needed for a 30mA RCD and 50V max sustained voltage.

EDIT: Some example values:
 
Its a chargemaster/ bp pulse unit... has to be my least favourite ev charger company, shocking customer service and damn awful charger units.
Its a personal victory for me when i remove one of those knowing its off to the skip and nobody else will have to endure it.

They were clever in getting in to garages and places early to offer 'free' installs or cheap installs but never innovated. the quality of installation though has in my view been shocking... sure some may be done well. but all the ones i have seen have been lacking.

The red button on newer units replaced the old jumpers to switch between 16/32A.
If damaged you may be able to replace it, but bp pulse/chargemaster are a closed shop and dont ordinarily supply spares outside the company. they will gladly charge a substantial call out fee and supply parts which when compared to a new unit such as a bg sync ev or evec unit i would go with a new unit.
 
That’s good to know that the 125 is within normal boundary’s.
I was worried that the installer maybe couldn’t get it down and just left it.

Yes wet Scottish soil, but rod and charge point right next to a road, so could be a bit hardcore-y

The button works… click in, click out… so I just cut out the damaged piece of wire and connected it. Just a bit shorter.
If the button had been fried, I would have just left connector with a link between.

How do you get into that charge point anyway? The key just turns the socket on and off.
There are a load of screws on the back of the front plate, but would need a dumpy Phillips to get them out.
 
That’s good to know that the 125 is within normal boundary’s.
I was worried that the installer maybe couldn’t get it down and just left it.

Yes wet Scottish soil, but rod and charge point right next to a road, so could be a bit hardcore-y

The button works… click in, click out… so I just cut out the damaged piece of wire and connected it. Just a bit shorter.
If the button had been fried, I would have just left connector with a link between.

How do you get into that charge point anyway? The key just turns the socket on and off.
There are a load of screws on the back of the front plate, but would need a dumpy Phillips to get them out.
they have a weird backplate where you need to remove various screws - used to be hex/security screws on some models to release it from the bracket, being located in the middle on base.
 

Reply to Overheating EV install in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
  • Article
Electrical2Go - Electric Car Charging at Home - Comprehensive Guide As EV ownership and the transition towards electric cars rise, having a home...
Replies
0
Views
139
Can we as electricians pick up on a broken PEN conductor? I’ve installed an EV charger for FIL, and everything tested fine, but there is a fault...
Replies
8
Views
2K
Had an EV charger installed in July last year. It’s wired directly off the mains. Since end of November anytime I plug the car in to charge, the...
Replies
48
Views
5K
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...
Replies
44
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock