I currently have a shop which has 3 phase 6mm cable running to it but the shop is only allowed single phase, currently renovating and they need more than a 32a supply. Can I parallel 2 of the 6mm and upgrade the quicklag breaker to a 50a at the MSB and make it a 50a main switch at the shops sub board. Both are same length and ran in one orange circular. In AS3000 I cant fjnd anythjng other than me being able to ruth them in parallel as they are 4mm or above.

Running new sub mains is what I'm trying to avoid for the client
 
When you say you have a 3 phase cable, do you mean a 3 core cable?
If so, you have not got enough cores to run a parallel supply.

You would need to have 4 or possibly 5 cores.
2 cores parallel for live
2 cores parallel for neutral
Possibly 1 core for earth,

It may be possible to use a ground rod or other method of earthing but I am unsure about regulations in upside down land.
 

Reply to Parallel sub mains in the Australia area at ElectriciansForums.net

Similar Threads

I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
583
Hi All, I’m after some advice. I’ll cut to the chase but I can give more detail if needed. A 400A sub main supply needs to be ran 100m, a pretty...
Replies
5
Views
2K
Was wondering if the gurus can critique and/or provide recommendations on my plan to install two sub-panels in a (50'x100') 5,000 sq ft steel...
Replies
2
Views
1K
Currently quoting for a job that needs to be done next week and working out how best to proceed, so thoughts welcome. Current situation: -->PME...
Replies
6
Views
4K
P
Hello, I have beens asked to do wiring in a new shop and there is a currently a consumer board supplying the building with all wires removed by...
Replies
11
Views
2K
peterl3986
P

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock