- Reaction score
- 8,889
Thank you. Section 514 re-read. One day it will sink in....Not required and hasn't been for a number of years.
Discuss Passing another circuit through back box in the UK Electrical Forum area at ElectriciansForums.net
Thank you. Section 514 re-read. One day it will sink in....Not required and hasn't been for a number of years.
Whats not required?Not required and hasn't been for a number of years.
A case of someone trying to make the regs fit their personal taste.Had a bit of a ‘discussion’ today with another electrician.
Basically found a light switch in which the radial cable for a socket directly below (but about 3ft lower) passed through.
Other electrician said it was wrong and shouldn’t be done.
My take was that it is, at best, a bit of bad design during the 1st fix. But other than that it kept the cable within the cable zone.
He argued that if the back box ever had to be replaced you’d have to cut the cable to the socket. To which I highlighted my point about bad design but that’s it.
To me it’s safe, cable is protected, it doesn’t interfere with the circuits for the lights (it was a 35mm back box) and it kept the cable within the prescribed cable zones.
He was adamant that it was wrong. I disagreed. He said it breached regs as you can’t have circuits feeding other accessories passing through.
So I asked what regulation it breached and why it was wrong. At this point the discussion ended as he couldn’t find the regulation in the ‘good book’ or OSG.
So, as I am always prepared to eat humble pie and admit if I’m wrong, does it breach any regulation to pass a seperate circuit through the back box of one accessory to feed another accessory? If so can someone let me know which regulation is contravened by doing so.
Thanks.
One of the biggest problems with this industry.A case of someone trying to make the regs fit their personal taste.
Whilst that may be true it is worth remembering 7671 is non-statutory and seen as a minimum standard. If you want to go over and above that you can.One of the biggest problems with this industry.
Too many try and pass off personal opinion/preference as a regulation.
Hence I now always ask what the regulation is that is being breached.
That's a whole new can of worms but just a little context.Whilst that may be true it is worth remembering 7671 is non-statutory and seen as a minimum standard. If you want to go over and above that you can.
Nothing wrong with a C3 and 134.1.1 - You could FI but this would fail the install and be deemed excessive. A C3 at least puts attention on it, even if thr client does nothing with it.
That can be true and yes you would hope you have more than 134.1.1 but its still an option, depends how how much it matters to either party as to whether or not to go down the route.That's a whole new can of worms but just a little context.
In this particular situation I returned to the job to find the fire alarm FP200 and the intruder alarm cables routed through my containment.
I could have been a real stickler (not the word I'd normally use ) and insist the whole lot was removed, or removed it myself.
Certainly there are black-and-white reasons why the intruder alarm cables could not be in there, its not open to conjecture, so these were pulled out and rerouted.
The amount of work involved in rerouting the FP200 was substantial, none of the cables would have been long enough. So, out of the kindness of my heart, I allowed them to remain.
If you're going pull apart other peoples work that is not in contravention of the BBB, and incur additional costs, you'd better have a better reason than "I don't like it, 134.1.1 poor workmanship" these things have a habit of escalating quickly.
Reply to Passing another circuit through back box in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.