Discuss Periodic IR testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
5
Hello all.
When conducting IR tests on condition reports, with L-N connected together and testing to earth. What equipment have you found will still cause the readings to be 0.00?
 
Hello all.
When conducting IR tests on condition reports, with L-N connected together and testing to earth. What equipment have you found will still cause the readings to be 0.00?

None, unless it's faulty.

An RCD spur or RCD socket can give a low IR measurement to earth, but not 0.00 Mohm.
 
Where in the install did you do the IR test? At the board I hope. If tested correctly then there is a fault. Test L-CPC and N-CPC to eliminate one or the other.

If it was tested at a socket etc then even with MCB open think PME could be the cause.
 
Well sounds like an appliance or the circuit has got an earth fault. Needs sorting.
 
Just had another look in this board, didn't realise there was a neutral link behind the main switch cover. It's a been converted to single phase from three.
So with the main neutral disconnected this time, testing the same way as before and testing each circuit individually I'm getting 0.23 on every circuit.
A couple test greater than >999 L-E but L with N together to E was 0.23.
Whats your thoughts fellas?
 
Just had another look in this board, didn't realise there was a neutral link behind the main switch cover. It's a been converted to single phase from three.
So with the main neutral disconnected this time, testing the same way as before and testing each circuit individually I'm getting 0.23 on every circuit.
A couple test greater than >999 L-E but L with N together to E was 0.23.
Whats your thoughts fellas?

Further investigation needed.
 
Just had another look in this board, didn't realise there was a neutral link behind the main switch cover. It's a been converted to single phase from three.
So with the main neutral disconnected this time, testing the same way as before and testing each circuit individually I'm getting 0.23 on every circuit.
A couple test greater than >999 L-E but L with N together to E was 0.23.
Whats your thoughts fellas?

Is this with each final circuit neutral disconnected and line disconnected (or circuit breaker opened)?
 

Reply to Periodic IR testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
587
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
393
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
633
Hi all, if I’m getting an insulation reading of 0.03 across N & L on a lighting circuit what would cause this? Neutral earth, live earth, are in...
Replies
12
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
827

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock