I have worked on a couple of jobs where back-up generators have been a requirement from the fire strategy document to power fire fighting lifts, smoke extract systems and sprinkler pumps. What particular requirements are you trying to find out?
 
Do somone know requirements for Permanent Diesel Generators Installed Inside a Building ?
Is this a Standby Set, or a Base Load set up? Things to consider:
Fuel Storage, tank bund needs to be sized so that it can contain all of the fuel in the storage tank, should there be a leak.

Signage, ensure all signage is up to standard.

H&S ensure you have the require First aid equipment.
Fire extinguishers, escape routes clearly marked.
Permit to work requirements, Adequate locks on doors etc, Only Authorised staff are allowed to enter unescorted.

Sighting of exhaust system, ease of access to building.
 
I have worked on a couple of jobs where back-up generators have been a requirement from the fire strategy document to power fire fighting lifts, smoke extract systems and sprinkler pumps. What particular requirements are you trying to find out?

I have worked on a couple of jobs where back-up generators have been a requirement from the fire strategy document to power fire fighting lifts, smoke extract systems and sprinkler pumps. What particular requirements are you trying to find out?

What about requirements for generator room dimension or does exist any particular regulations for it.
 
I would suggest contacting a generator supply company. The company we use are the wrong end of the country for you but try Dieselgenerators.co.uk they are based down in the South of England.
 
What about requirements for generator room dimension or does exist any particular regulations for it.

As David mentions, contact a specialist as they will give you the minimum clearance required around the generator for maintenance purposes, there are no regulations that give guidance on the room size.

In addition to the need to vent the exhaust, you will also need to provide supply and extract air to the room to enable the generator to maintain its temperature. The supply air duct is typically a bell mouth opening positioned next to the radiator.
 
Other things to consider are is this located on the ground floor? i.e. you don't want to be designing an installation where the end users has to transport fuel up the stairs or in a lift - CDM issues.

Where will the exhaust vent to? i.e. if its through a wall which backs onto a public foot path, the local authority will not like it.

Will noise from the generator cause issues with the locals?

If you could give us more information it would help.
 
Ok you really need to offer up more information if you want help with this.
The lads will happily answer your questions but please give them a bit more to go on.
I think there are a page full of replies asking you for clarification so maybe answer all those first.
 
I have to make a design for generator room with all installations ( ventilation, air supply, exhaust) and obviously all wiring
Don't forget EM lighting either, non slip flooring, emergency exits large entry doors for getting large equipment in and out.
 

Reply to Permanent Diesel Generators Installed Inside a Building in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all. Slightly out of the ordinary, but I'm looking to replacing between 60 to 100 standard size E27 bulbs with LED equivalent. The catch is...
Replies
3
Views
323
I'm an electrical engineer in training so please bear with me. Basically, a bank has ordered a second 500kw diesel generator and my job is to...
Replies
3
Views
889
Metal building with living quarters the panel is on the outside and about 20 feet away from new build that will be 2x6 what type of shielded wire...
Replies
3
Views
533
I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
278
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock