Discuss Permanent live for smoke alarms and emergency lighting in the UK Electrical Forum area at ElectriciansForums.net

Neptune

DIY
Reaction score
24
Need some guidance please.
I know that smoke alarms require a permanent live and neutral in order to operate. Is this also the case with emergency lights? (The type you have in stairways)

Secondly, have I also understood correctly that these two can only be available at the ceiling rose if the loop has taken place in the ceiling? I.e. if the loop is at the switch, I will have a neutral at the ceiling but not a permanent live?

Thanks in advance.
 
Thanks for your help.
Thinking this through, I will need to take a connection from wherever the loop is done i.e. ceiling or switch as this is where I will find the permanent live and neutral. Have I understood this correctly?

Also, whilst I am at it...could I take a feed (permanent live, neutral and CPC) and supply it to a AICO smoke detector first and then to the emergency light? This may be an opportunity to include a mains powered smoke detector too.
 
You need to remember the emergency light needs a test facility so this mustn't isolate the smoke detector. BS5266 has all the requirements for the provision of emergency lighting it isn't something which should be done ad hoc, it is a safety system.
 
If this is a standard UK ceiling rose then you will have a permanent line and neutral available at this point. Even if the rose has been replaced with a newer light fitting there will often be a L&N available.

b7a0303c407814ee17b6d90d37fd5bb1.jpg


I would certainly recommend AICO radiolink units, no messing around with an interlink cable between bases.

As mentioned, emergency lights fall under BS5266, is this for a commercial property as part of a fire risk assessment or for your own home?
 
If this is a standard UK ceiling rose then you will have a permanent line and neutral available at this point. Even if the rose has been replaced with a newer light fitting there will often be a L&N available.
Presumably not if the loop is at the switch? I thought it was a mixed bag in terms of whether the loop has been done at the switch or ceiling in the UK.

As mentioned, emergency lights fall under BS5266, is this for a commercial property as part of a fire risk assessment or for your own home?
It's an odd one. I am a freeholder of a block of flats (3 Storey Victorian house) but each floor is owned by different individuals. As I understand it, they have an operational smoke alarm in each of their flats as do I, in the top most flat.
I am unclear on whether it is legally required but I wanted all three of us to fund emergency lights and smoke detectors on each floor for added protection. Hence the questions on how they could be wired.

I would welcome any further suggestions. Thanks again.
 
Presumably not if the loop is at the switch? I thought it was a mixed bag in terms of whether the loop has been done at the switch or ceiling in the UK.


It's an odd one. I am a freeholder of a block of flats (3 Storey Victorian house) but each floor is owned by different individuals. As I understand it, they have an operational smoke alarm in each of their flats as do I, in the top most flat.
I am unclear on whether it is legally required but I wanted all three of us to fund emergency lights and smoke detectors on each floor for added protection. Hence the questions on how they could be wired.

I would welcome any further suggestions. Thanks again.
Modern installations could be run via the switch however the vast majority are still looped at the light and have a neutral run to the switch. This allows the circuit to be tapped for smokes etc and have smart switches installed if required.

I'm not up to date on the latest requirements in your instance so anything I say would be pure guess work... ? But a lot would depend on how the flats are built and the fire compartments are designed.
 
Modern installations could be run via the switch however the vast majority are still looped at the light and have a neutral run to the switch.
I can concur that most older installations are looped at the ceiling. When this is the case, I find this configuration:
1637754808507.png


I note that this doesn't take a Neutral to the switch but you suggested that it does. Incidentally, this then presents issues with smart switches as most require a neutral wire.
Can you please clarify?

Thanks for your help.
 
I can concur that most older installations are looped at the ceiling. When this is the case, I find this configuration:
View attachment 92283

I note that this doesn't take a Neutral to the switch but you suggested that it does. Incidentally, this then presents issues with smart switches as most require a neutral wire.
Can you please clarify?

Thanks for your help.
Only in recent years has BS7671 recommended running a neutral to the switch position to allow for future upgrades. You can get smart switches that work without a neutral but for the cost of a few meters of cable on a new build or rewire it makes sense to run a neutral in. Ideally the ceiling rose should be updated to allow for four cables rather than three but this is down to manufacturers etc to sort out.

So older installations there will be no neutral ran to the switch, sorry if I added confusion.
 
Makes sense now. Can you forward me a wiring diagram of the neutral being carried across to the please? I am wondering if this is then a 4 core cable...
on new work, you would generally use a 3 core/E cable from light to switch in order to provide a N at switch.
 
on new work, you would generally use a 3 core/E cable from light to switch in order to provide a N at switch.
Where on the switch would this new Neutral wire connect?
Also, can I please confirm that you are proposing a 3 core and earth cable from the light to the switch under this configuration.
 
Where on the switch would this new Neutral wire connect?
It wouldn't normally, you'd put it in a connector block unless you were using a newer switch that has a provision for a neutral link on the actual light switch fitting.

Also, can I please confirm that you are proposing a 3 core and earth cable from the light to the switch under this configuration.

Personally i don't understand the comment about 3 core for an N at the switch, you can just do that with T+E. T+E feed in, T+E out to light, CPC N and SL all present.

Unless you want to use 3 core to put the perma live from switch to rose in order to loop in from the rose to the next light. Sure Telectrix will clarify (i am only a meagre apprentice at present.) EDIT: I get what he's saying now, i was thinking about it from a 'take from the switch' perspective not taking the feed to the rose.

That said, i would just get an electrician out to have a look. No point guess working it when you can just pay an expert to sort out the plan in about 10 minutes.
 
Last edited:
It wouldn't normally, you'd put it in a connector block unless you were using a newer switch that has a provision for a neutral link on the actual light switch fitting.



Personally i don't understand the comment about 3 core for an N at the switch, you can just do that with T+E. T+E feed in, T+E out to light, CPC N and SL all present.

Unless you want to use 3 core to put the perma live from switch to rose in order to loop in from the rose to the next light. Sure Telectrix will clarify (i am only a meagre apprentice at present.) EDIT: I get what he's saying now, i was thinking about it from a 'take from the switch' perspective not taking the feed to the rose.

That said, i would just get an electrician out to have a look. No point guess working it when you can just pay an expert to sort out the plan in about 10 minutes.
Are we in agreement that a 3 core and earth cable would be required for this approach (from light to switch) and the neutral wire would be terminated in a wago behind the switch - in anticipation of smart switch, etc.
 
Are we in agreement that a 3 core and earth cable would be required for this approach (from light to switch) and the neutral wire would be terminated in a wago behind the switch - in anticipation of smart switch, etc.
If you mean taking the feed to the light fitting and needing a neutral at the light switch then yeah, it just makes sense to use 3core+e or 4 core and use the black as the switch live and grey as the neutral with sleeving. Shove the grey into the neutral bar on the ceiling rose and wago the other end.

Or, tell your electrician to do that, i mean.
 
the wholepoint of 3 core/E is to have all possibles at both light and switch. i/e/ L. / S/L / N / E. then there's no chasing out of Mrs. Bloggs's new decor when she decides on some smart tat.
 

Reply to Permanent live for smoke alarms and emergency lighting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
Hi all, I have two questions regarding wiring and containment on commercial property stairwells in Ireland. We are currently wiring a 3 story...
Replies
10
Views
703
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
659
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
455
Hi All, Please may I ask if light fixtures must now always be fitted by an electrician? also for domestic homes, is it okay for there to be a...
Replies
4
Views
784

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock