Hi folks,

I'm carrying out an EICR on a 3-Ph board which cannot be isolated fully - only certain circuits at certain times. Supply protected by 3x 88-2 fuses.

When carrying out PSCC/PFC, I'm getting a small spark at the probe on the neutral bar/MET intermittently. Can anyone explain this? The test is being carried out at the origin. Could it be anything to do with the fact that some of the circuits are under load at the time of testing? I am aware that to do things by the book, the board itself should be isolated. The results aren't overly massive - around 6.9kA (13.8kA Phase to Phase).

Many thanks in advance.
 
in doing the test. you are drwawing current through your mft. a small spark is normal
 

Reply to PFC measurement question in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Where do people record the Ze & PFC of a 3 phase installation, if there is say 10m of 25mm tails between the 4 pole isolator (next to the meter)...
Replies
7
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
664
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
748

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock