Discuss “Phantom” Short on radial circuit in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi,

I’ve been recently working on a living trailer for a friend, when they have the supplies connected (240VAC 16A) they have nuisance tripping on the RCD. I’ve traced through and found an outside waterproof socket to be at fault, short circuit between live and earth. Removed the socket and tested, fault was not on socket, short still within the wiring. So I traced the cable back to a small joint box about 3M away. When I disconnect the cable from the box, then test of both sides of the connection box, there is no short. But as soon as I wire the cable back up the short comes back. I’ve completely removed the connection box and used inline crimps (to eliminate the connection box for testing) still the short is there. But when all is disconnected, each cable is fault free. Only when everything is connected will the fault reappear?

Any ideas?
 
Could it be that moving the cable is causing/breaking a short elsewhere (e.g. hole without grommet, etc)?
[automerge]1597144464[/automerge]
Also are you testing with an insulation resistance sort of meter (i.e. a "Megger" or similar that uses 500V) or a multimeter?
 
Could it be that moving the cable is causing/breaking a short elsewhere (e.g. hole without grommet, etc)?
[automerge]1597144464[/automerge]
Also are you testing with an insulation resistance sort of meter (i.e. a "Megger" or similar that uses 500V) or a multimeter?
I thought it was the cable, but was testing it while moving it round and especially around the gland areas, no luck.
Was using a multimeter at first, then IR tested it, no problem on either end while disconnected >999
 
TBH I'd replace the cable, could well be insulation damage that only shows when in certain positions.
 
The fault may be from L in one leg of cable to CPC in the other, so each cable tests good by itself. As Static points out, the CPC in one leg may not be connected to the chassis. If the L on that leg is faulted to the chassis only, it won't show up on its own CPC but it will via the chassis to the CPC of the other leg. Test all to chassis and each other, not just each cable separately.
 

Reply to “Phantom” Short on radial circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
666
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
410
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
848
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock